converting back to NG
michael225q
Member Posts: 7
in Gas Heating
Replaced the gas valve and pilot valve with new . need to do something with the main jets . They are #57 for LP need #50s for NG, Can I drill them out ? What size drill for a #50 jet ? Slant Fin Victory series V-120
0
Comments
-
What is the input to the unit? How many burners are there? What is the outlet pressure from the gas valve? How did you come to those numbers for LP and Natural gas? Do you have a combustion analyzer? If so be sure and do an analysis after the conversion.0
-
Oh ! I just figured it out . The jet size is the drill size and I got the info size from the install manual on the high altitude page.0
-
Still answer my questions so we can make sure .0