Williamson GWI gas boiler

Is there a reason the manual states the expansion tank must be in the return piping.
0
Leave a Comment
Categories
- 80.9K THE MAIN WALL
- 2.5K A-C, Heat Pumps & Refrigeration
- 36 Biomass
- 394 Carbon Monoxide Awareness
- 2.6K Controls
- 1.4K Domestic Hot Water
- 3.7K Gas Heating
- 101 Geothermal
- 130 Indoor-Air Quality
- 2.3K Oil Heating
- 30 Pipe Deterioration
- 564 Plumbing
- 4.2K Radiant Heating
- 333 Solar
- 12.1K Strictly Steam
- 36 Water Quality
- 7 Industry Classes
- 53 Job Opportunities
- 7 Recall Announcements
Comments
itll work fine there with the circulator on the supply....the main thing is to pump away from the "point of no pressure change" (expansion tank) this is so the circulator will move water by increasing its discharge pressure....its for better air removal.....i see installs piped improperly and i have to go back every year to purge air out of the system.....i have yet to go back on my sysyems for that problem....and the feed valve should always be located at the expansion tank connection.