Triangle Tube Prestige 155 ACVMAX / 60 gallon indirect DHW install

cpb282
cpb282 Member Posts: 8
Greetings, I'm about 30 miles north or NYC and just had a Triangle Tube Prestige 155 ACVMAX installed with a 60 gallon Smart indirect DHW this past week. We have baseboard convectors, 3 zones. I'm curious as to what you all think of the installation (the good, the bad, and the ugly). See the link to the video below.
It replaced a 1960s steel boiler (AGA output 140k btu/hr, net output 123k btu/hr).

https://youtu.be/QYgKGnuLNIA

Thanks,
CPB

Comments

  • Robert O'Brien
    Robert O'Brien Member Posts: 3,563
    I think it's way over sized! :)
    To learn more about this professional, click here to visit their ad in Find A Contractor.
    Paul S_3Ironman
  • cpb282
    cpb282 Member Posts: 8
    I was a bit concerned about that. Their initial gut reaction was a 175. I said I thought that was large. They said they did a heat loss calc and said that I was right, and suggested a 155. I don't have results of the heat calc. It may end up working out as we're considering an addition down the road (not that the installer knew that).
  • Paul S_3
    Paul S_3 Member Posts: 1,280
    sq ft of home?
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • cpb282
    cpb282 Member Posts: 8
    2,500 SF colonial built in the mid 1960s.
  • cpb282
    cpb282 Member Posts: 8
    By the way, Paul. I was born and raised in SI, on the north shore.
  • Paul48
    Paul48 Member Posts: 4,469
    Wayyyy Over-sized
    kcopprick in AlaskaSWEI
  • cpb282
    cpb282 Member Posts: 8
    I did have another contractor do a heat loss calc and he suggested 110, which is why I reacted to the 175 as being oversized. I appreciate the opinions - this is a learning experience for me.
  • cpb282
    cpb282 Member Posts: 8
    I guess not much I can do about it now other than make it be a learning experience for others. I feel better that I pushed back on the 175 and that it is a modulating boiler (I considered an atmospheric).
  • Ironman
    Ironman Member Posts: 7,550
    The workmanship looks fairly neat, but as others pointed out, the boiler is twice the size you need. This will result in shorten boiler life and less efficiency.

    I would recommend that you download SlanFin's heat loss app and do your own calc. Then make the contractor produce his. I seriously doubt that they did a proper one based on ACCA manual J. Then tell them they can either remove the present boiler and install the correct size or add a properly sized buffer tank at their own expense.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
    KC_JonesSWEI
  • cpb282
    cpb282 Member Posts: 8
    I appreciate the suggestions. Will the fact that it is a modulating boiler reduce short-cycling?
  • cpb282
    cpb282 Member Posts: 8
    Thanks. I'll see what they say and will report back.
  • Bob Bona_4
    Bob Bona_4 Member Posts: 2,083
    Obscenely too big, Chris. Your heat loss was 69,985.
  • Bob Bona_4
    Bob Bona_4 Member Posts: 2,083
    He's at 2400 Sq ft. One room was a garage, likely on sleepers from the elevations. 11, 153 loss there. Another notable was a dual fireplace in the kitchen and the living room on opposite side (15,000 kit, 12, 612 lr). Rest of the house was typical.
  • Bob Bona_4
    Bob Bona_4 Member Posts: 2,083
    edited September 2016
    I'm plugging in slab on grade, with 2 outside walls, no edge insulation. 2 full outside walls, and a partial third. 400 Sq ft area. Ventilated attic with R 19 above. Kitchen has a long exposed wall with 2 windows and a slider. Living room has 3 exposed walls, 2 which have windows. Kit and Lr are over unheated basement.

    Loads are fun bc you catch areas that at first seem not that consequental, bear a closer look.
  • Paul48
    Paul48 Member Posts: 4,469
    That's a shame, because there is equipment available at his heat loss that is really well matched with better range. It never ends!
  • smithfan
    smithfan Member Posts: 91

    Unfortunately not.

    The boiler reduces its supply water temperature as the outdoor temperature climbs. This has the effect of making the emitters (the baseboards) smaller. They put out less BTU's with lower water temperatures.

    The boiler also modulates itself as necessary to feed the baseboards. However, the problem occurs when one zone calls and needs, say 8,000 BTUH. The boiler has a minimum output of 25,000 BTUH. So, it quickly reaches its temperature setpoint and shuts down.

    The 80 has a minimum firing rate of 14,400 and it, too, will be too large for a single zone in warmer weather. However, it's far more manageable than 25,000.

    The best thing you could do with that boiler, short of getting it replaced, is to eliminate the zoning. When one zone calls, all zones get flow. You balance the house with a set of valves to keep the temperatures in all zones approximately equal.

    ^^ This is essentially what I do with my 110 on a house half the size, about 1400sf, my zones are not combined, so I try and run them succinctly as much as possible. The idea is to get as much water volume running through your system as possible to avoid short cycling. If you got the time and expertise just combine the zones into one if not, run them together as much as possible. It's a constant battle with over-sized units!!