How Did they get the air out in 1963?
JUGHNE
Member Posts: 11,279
......This was supposed to be on the Main Wall.....
I have a boiler of that age that I just cleaned up. The state boiler inspector gave the boiler his blessing today.
It had been drained and sat idle for one season. Thankfully only one pipe froze. The building boiler room is on grade. The piping goes up into the attic. and drops down to commercial BB convectors. I have seen no air bleed ports in the attic. There are no isolation valves on the S&R--2 1/2" copper lines. No air bleeders on the convectors that I can see. They are actually the low point of the system so I assume the air is in the attic piping.
We have the larger 3-piece B&G on the return pumping into the lower boiler tapping, water fill is connected between pump & boiler.
The supply comes out the top side tapping thru a B&G ABFSO 4" X 4" with 3/4" up to ATF 18 Airtrol on compression tank bottom.
The horizontal line to the AFT 18 now has good slope up towards the tank.The pump is trying to move a lot of air.
I realize the best way would be to isolate the boiler and fast fill the system dumping the air/water. However there are no ports available to do this. This is thought to be needed for maybe two years until a new nursing home is built.
Somehow this system has worked since 1963, the air must have been purged somehow. I have another 1961 system piped the same way and have gotten the air out much quicker than this case. Any thoughts appreciated.
I have a boiler of that age that I just cleaned up. The state boiler inspector gave the boiler his blessing today.
It had been drained and sat idle for one season. Thankfully only one pipe froze. The building boiler room is on grade. The piping goes up into the attic. and drops down to commercial BB convectors. I have seen no air bleed ports in the attic. There are no isolation valves on the S&R--2 1/2" copper lines. No air bleeders on the convectors that I can see. They are actually the low point of the system so I assume the air is in the attic piping.
We have the larger 3-piece B&G on the return pumping into the lower boiler tapping, water fill is connected between pump & boiler.
The supply comes out the top side tapping thru a B&G ABFSO 4" X 4" with 3/4" up to ATF 18 Airtrol on compression tank bottom.
The horizontal line to the AFT 18 now has good slope up towards the tank.The pump is trying to move a lot of air.
I realize the best way would be to isolate the boiler and fast fill the system dumping the air/water. However there are no ports available to do this. This is thought to be needed for maybe two years until a new nursing home is built.
Somehow this system has worked since 1963, the air must have been purged somehow. I have another 1961 system piped the same way and have gotten the air out much quicker than this case. Any thoughts appreciated.
0
Comments
-
Sure there is not at least a t with a plug you could crack open in the overhead piping?
0 -
No, not sure, have been waiting for cooler weather. There is about 10" of blown in insulation covering things....plus air handlers, ductwork etc.
I have found only 3 of the 7 zone valves.....3 of the 7 have no power to the T-stat. One with no power did seem to heat up, the valve must be manually opened.
If nothing is found, any recommendations for drilling/tapping a port into 2 1/2" hard copper.....not sure if L or M.0 -
Petes plug?0
-
-
-
Thanks for all replies. Will get back there when the attic cools off. Will keep you posted.0
-
You can drill into the tube anywhere and braze in a copper stub. Properly done that will never fail.0
-
Do you think that "Stay Brite" soft solder would do the tap connection......trying to avoid the big torch in the attic.
I might try one in the bench vise in the shop.0 -
You don't use C-tanks for oxy-ace? I like those in a small holder to carry into attics. Along with a bucket of water and heat shields.
I have reservations about any type of soft solder. It is really hard to build enough of a bead to get more mating surface.0 -
-
My hesitation on that is probably unfounded as the pump is below the water level of the system/boiler. I have to convince myself that the impellor will always be wet, even while pumping air/water mixture, there is little possibly of pump damage...yes?Each time the pump is switched off and restarted I hear more air being pushed into the boiler.
However there is the chance of having to drain the system for zone valve repair in the attic, perhaps several times.
Again, just fishing for ideas and appreciate any heads up points.
It is 40 miles away and I have been pretty spoiled having most of my work within a 3 mile radius.0 -
-
Of course you could help things along w the ME trick.... A cup of dishwashing soap pumped into the system0
-
I have heard of that, but one should clarify if this is Dawn Liquid as you put into the sink for hand washing dishes......or Cascade crystals that actually go into the DW appliance.
When one son was about 10 years old he demonstrated what Dawn liquid does in the DW. It becomes a great foam machine!
0 -
I have had great luck pulling a vacuum on a dormant system with little water in it. It's my preferred way for most commissioning actually. New installs especially. Pull vacuum for a few hours after air testing for system tightness and the water will go into pretty much all the piping. This is of course after capping all the auto bleeders. Then run circulator on a cold system for a few hours/days.
TaylorServing Northern Maine HVAC & Controls. I burn wood, it smells good!0 -
Same here. You can go nuts bleeding air piecemeal.Solid_Fuel_Man said:I have had great luck pulling a vacuum on a dormant system with little water in it. It's my preferred way for most commissioning actually. New installs especially. Pull vacuum for a few hours after air testing for system tightness and the water will go into pretty much all the piping. This is of course after capping all the auto bleeders. Then run circulator on a cold system for a few hours/days.
Taylor
0 -
Thank you, Kcopp & Gordy, today I did run the pressure up to 25PSI and the pump did grab the air and pass it. I did run the boiler up to 150 just so I could feel pipes warming up.
Getting heat to most of the BB now,
I will try more tomorrow. It had to run about only about 3 hours before the water started to move.3
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements