Taco 2218 tight fit..
john p_2
Member Posts: 367
Need to know how many diameters of straight pipe are required (minimum) on the inlet & discharge side of the pump...I see nothing in regards to this with paperwork that comes with the pump.
0
Comments
-
-
you can practice the same installation recommendation used with commercial installations; 10 pipe diameters up, and 5 down. That should minimize turbulence at pump which could cause inefficiency in performance. Please contact me directly if you have additional questions.Joe Mattiello
N. E. Regional Manger, Commercial Products
Taco Comfort Solutions0 -
As Bob mentioned above, what you should do and what actually gets installed and works, often differ.
A classic example is the internal check valves that pump manufacturers install or include. Those also should be a fair distance from the discharge, as per accepted piping practices, yet they get installed directly in the volute. I've not seen or heard of problems.
Or the pre-packaged GEO modules with two to four circs, often high head models, bolted flange to flange, yikes! Talk about a conflict of turbulence )
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Wow, 10 diameters (12"1/2") yikes! That's tough in my install.....but thanks , good info.0
-
John is doing a 2 pipe buffer Bob's . his header between the boiler and tank is 1 1/4" , design load is under 70 k at design and he is extensively zoned , 5 or 6 zones I believe with a couple very small zones . He is re fitting with the buffer because of excessive cycling . Boiler is Utica SSC 75 , 60 gallon Utica H20 buffer . The VT is being used in Delta T mode and is being moved due to piping configurationYou didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38330 -
Thanks Rich...0
-
I would caution you about that header size, generously sized is the suggestion. You want the flow velocity in that header pipe as close to zero as possible. What is the required flow rate at design? Lets assume 7 gpm for that 70K boiler load.
I know it sounds overkill but 2" is a definite, 1-1/2 close, 1-1/4 a tad small perhaps, you may experience some unwanted or ghost flows or mixing.
Use the dimensioning on a hydrosep as a guide line. Our 1" sep, for example, rated for 11 gpm has a 3" barrel. That should get that flow velocity in the sep body down around .5 fps or less, under 1 fps for sure.
We have done a lot of engineering and flow testing on separator design to assure you get the results you need and expect, don't tempt fate.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
1 1/4" is fine Bob . His average flows through the header are less than 4 gpm with very short excursions above that flow rate . 6.5 would be the absolute max flow with all zones calling at design . Maybe 2 hours a year . Thanks for the inputYou didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38331
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements