0ld pimary oil burner control ( Honeywell - R4184D ) upgrade.
ppllgg
Member Posts: 69
I hear the Honeywell Flame Safeguard is a excellent replacement & upgrade, Does anyone know of the part # of that. or make & model of the one I would need ??
Regards,
Frank S.
Regards,
Frank S.
You can use this:
s3.supplyhouse.com/product_files/R7284-INSTALL.pdf
but take special note of the wiring diagram for use with a line voltage thermostat--IOW, don't wire line voltage thermostat to T-T on control.There was an error rendering this rich post.
1 -
Thanks Steve for your MUCH Appreciated Help .... Could you explain about the line voltage thermo. & The T-T control ? (I'm not that familiar with this...)0
Is this on your older Burnham RS boiler?
Consulting0 -
Yes, as Steamhead asked, what kind of equipment do you have.
Boiler-make/model
Burner-make/model
Aquastat-make/model
...Could you explain about the line voltage thermo. & The T-T control ? (I'm not that familiar with this...)...
I (collective we) can only help so much. If you unsure with wiring, best let a pro come in and do the simple replacement. If you make a mistake, then you buy another control. 2 controls at your price isn't much cheaper then a pro coming in and doing it.There was an error rendering this rich post.
Thanks for your prompt reply Steve &Steamhead !!
It's a Burnham RS -111-T-TB
S/N 8899035 series WV-18-9A
Burner is a Beckect Mod. AF
I'm not sure what the "Aquastat " is or does ...It does have the other cotrolbox (above it )its also a Honeywell that deals w/ Hi-Low water temp.settings & a thermostat upstairs.
And there seems to be (4) variations of this R7284 ...B, P, U or G ?? I'm assuming I'd be using the (U) model (Universal).
Thanks, Your help IS GREATLY Appreciated !!
OK- how long do you expect to keep this boiler in service, before replacing it?
Consulting0 -
As long as it doesn't leak, I just replaced the complete comb. chamber. & it runs & performs nice ( except for this intermittent ignition prob. that went away when I cleaned the contacts on the relay in the prim. control. that why I want to upgrade that control. Prob. will probably recurred sooner than later.0
OK- assuming your burner does not have a solenoid oil-delay valve, the simplest alternative is the Beckett 7505A-0000 which directly replaces your current control, with two exceptions: 1- it shuts off the ignition after the flame is established, saving electricity and wear, using separate connections for the ignition and motor, and 2- you will have to install a jumper wire across the thermostat terminals. Also, it has the current 15-second lockout time rather than the old control's 45 seconds, which is far safer. If you absolutely can't have a pro handle this, the 7505A-0000 should keep you out of trouble.
If an older boiler is to stay in service for a while, I like to add an oil-delay valve which cleans up the starts and stops, reducing soot buildup, simplifying future maintenance and improving the unit's seasonal efficiency. This is where a more-sophisticated control like the R7284 earns its keep. All new oil burners come with this setup. But I do not recommend that a non-pro handle this type of upgrade. It has to be done just right.
After any type of work on any combustion unit, be it oil, gas, pixie dust or whatever, a digital combustion test is mandatory. If you don't test, you're guessing- literally "playing with fire". This is another reason to have the right pro handle your burner.Baltimore, MD, USA
Consulting0 -
just curious..when was the last time it was tuned up? maybe get a tuneup done and have the part on hand for them to install...just a thought..:)0
THANKS STEAMHEAD & Ichmb for that Excellent Advice !!
Do you know of any Central CT. HVAV Pros as your self you can recommend ?
Regards,
FRANK S.
What town in ct are you in?0
Good choice. Can't hurt to call him:Paul48 said:@Charlie from wmass
Maybe Charlie could take a ride down 91?
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heatingBaltimore, MD, USA
Consulting0 -
I'm in Southington , Ct. 064890