boiler burners, flame and pressure
aircooled81
Member Posts: 205
When the manufacture calls for 3.5" manifold pressure, what is the lowest pressure to allow at the manifold?
I have a boiler that has the yellow tips of the flames touching the cast iron sections of the boiler, and I am thinking of adjusting the burner pressure lower, to lower the flame height with-out losing blue flame.
Any suggestions?
I have a boiler that has the yellow tips of the flames touching the cast iron sections of the boiler, and I am thinking of adjusting the burner pressure lower, to lower the flame height with-out losing blue flame.
Any suggestions?
0
Comments
-
Usually 3.5" is the maximum. Check the burner tubes, make sure they're clean inside and out. Do this before making any adjustments.0
-
Without the proper equipment to monitor pressure (which should be what the manufacturer calls for, within a very small margin) and the combustion -- CO, CO2, excess O2, temp, all that good stuff -- playing with burner settings is chancy at best. IMHO.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England1 -
cleaned the burners, checked gas pressure with manometer.
no combustion gas analyzer, so the consenses is leave it at the manufactures spec - or the posted spec on the nameplate is the max.
any opinions on flame height and impingement on the cast iron sections?0 -
If you don't have a combustion analyzer you're wasting your time.To learn more about this professional, click here to visit their ad in Find A Contractor.0
-
Agreed. Sure, analyzers aren't cheap, but they're much cheaper than lawyers.Robert O'Brien said:If you don't have a combustion analyzer you're wasting your time.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
Can you recommend a good model analyzer?
I looked at and have used the filedpiece sox3, but it doesnt do co.
0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements