Steam Pipe Insulation per Code Requirements
PaulVW
Member Posts: 2
In 1 of the cities I service, the city is requiring all new pipes on replacement steam boilers to be insulated even if none of the other pipes are insulated. I understand the value of insulating steam pipes but I believe I read or heard in one of the Don H seminars that it was a bad idea to insulate the wet return on a 1-pipe steam system. As I remember the condensate needs to lose some heat before it gets to the close nipple of the Hartford loop to reduce flash steam and banging. I looked through “Lost Art of Steam” and could not find it. (I do need to buy a new book, it was bought in 1993 and is quite worn...) Please let me know if I’m on the right track, I have to document it for the inspector.
0
Comments
-
The condensate in the wet returns should not be that hot in the first place -- one pipe or two pipe. Further, the pressure at the Hartford loop -- applied by the equalizer -- should be high enough to prevent any possibility of flashing.
In my opinion and understanding, anyway...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
Paul, I believe condensate returns and better off insulated. As water cools, it absorbs carbon dioxide, which results in carbonic acid that rots pipes.Retired and loving it.0
-
My wet return runs much hotter now that I insulated the dry returns especially when it's very cold out. Not sure how hot, but too hot to touch.
I wish I could insulate the wet return, but it's placement makes it kind of difficult if not impossible.
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements