“Vacuum Boost” for steam heating system

Here's a great paper from the brilliant mind of our friend, Igor Zhadanovsky. Thanks for sharing, Igor!
President
HeatingHelp.com
HeatingHelp.com
1
Leave a Comment
Categories
- 80.9K THE MAIN WALL
- 2.5K A-C, Heat Pumps & Refrigeration
- 36 Biomass
- 394 Carbon Monoxide Awareness
- 2.6K Controls
- 1.4K Domestic Hot Water
- 3.7K Gas Heating
- 100 Geothermal
- 130 Indoor-Air Quality
- 2.3K Oil Heating
- 30 Pipe Deterioration
- 562 Plumbing
- 4.2K Radiant Heating
- 333 Solar
- 12.1K Strictly Steam
- 36 Water Quality
- 7 Industry Classes
- 50 Job Opportunities
- 7 Recall Announcements
Comments
This sounds like a Paul air line system. The vent valves with air lines are called, oddly enough, "Paul valves".
Would you happen to know what type of controller starts and stops the vacuum pump?
What vacuum levels are maintained on the 3/8" air lines?
And finally, what type of vacuum pump is used on this system?
Website: www.nashjenningspumps.com
The first step in solving any problem is TO IDENTIFY THE PROBLEM.
In my first setup the air was pushed through bimetal valve - check valve combo on each radiator and later run in naturally created vacuum. With time those valves started to fail and deteriorated system performance, - it's a reason why I started tinkering with vacuum pump.
It will be interesting to have a look at the one pipe vacuum system in Montreal and check for simplification.
When working on refrigeration piping I pull a vacuum from a single location (sometimes through 6-8 ductless coils), after reaching 500 microns I close the line to the vacuum pump (before turning it off) and fill the system with refrigerant.
If the vacuum is is first mechanically induced before the burner fires, then the air vents will only be venting oxygen that separates from the water and if air finds a way in through leaks during operation.
Might be simpler not to run separate vacuum lines, only use the pump for charging the radiators and let the steam maintain the vacuum. Or maybe I'm missing something.
Whatever the best way is, there's no doubt in my mind that I'll be installing Central steam heating systems.
After trying various soft elastomer coated seats and clappers, along with Nylon and Teflon, including valves specially made for vacuum service, I'm coming to the conclusion that old fashioned metal-to-metal construction is the best choice today, if it's air tight to begin with.
There's no question that something better is needed, but being a mechanical device with moving parts, it's going to wear out eventually.
Website: www.nashjenningspumps.com
The first step in solving any problem is TO IDENTIFY THE PROBLEM.
"If something sounds to good to be true it probably is"
But then again, I think this has a shot.
With what sounds like a few hundred dollars in parts, I think I'm just going to go try it and surprise my next steam customer.
There are some subtleties in seemingly simple vacuum heating system . Would you mind letting me know more detail of your project?
I'm still waiting to hear from the home owner I last talked to that had Mickey Mouse the shoe maker working on his steam system for 30 years.
I talk to people every where I go trying to find steam systems.
Trying to think that through, makes my head hurt. How do you prevent the vacuum source from becoming the highest vacuum in the system? I understand the Paul system, as it puts the source where you want it, at each radiator, but generalized vacuum, I don't get. Can you explain the sequence of operation, so I might grasp it?
The way I understand/remember some steam heated buildings in Toronto fifty years ago is that they were no vents anywhere but a single vacuum generator. With no traps and no vents differences between one pipe and two pipe loses significance. In boiler room was a city water powered eductor. Periodically operator isolated boiler (butterfly valves I think) and opened valves from steam pipes to eductor. Then he turned on city water -in winter Toronto water is cold- and sucked down to over 28" vacuum. Finally he isolated eductor; re-opened boiler valves; energized burner.
I'm not certain.....I think evacuation was done only when boiler water temperature was deemed too high.
The point is that if there are no traps,whole heating system is connected and air can be removed from anywhere.Traditional two pipe vapor systems eventually eliminate air and then work beautifully for decades.Why not one pipe?
"Where's the vacuum?" Or "Why's the condensate pump to vented receiver running all the time?" The pumps lose prime in the latter circumstance. [it's a big system with boiler feed for multiple boilers-- no passive return here]
It's getting to where I specify unions at checks so they can be replaced every 2 years. I don't remember this being quite so epidemic in the past.
Maybe it's what @Pumpguy is getting at: the very old check valves were metal to metal seals so would last a long time. I'll seek out the old fashioned kind before they became "new and improved."
Probably need a butterfly valve to stop the steam when the house is satisfied.
Please someone explain how the Latent heat goes up with the deeper vacuum.
Sorry, have to repeat this
Some thoughts about heat distribution in a vacuum system. In regular steam system local vacuum spots are created (by steam condensation) and moved from the boiler to the radiators at a total pressure of 1‐2 psig within a regular steam system. From one side of this local vacuum spot, steam is supplied by the boiler‐ from the other side, air from the air vent. Thanks to this, the pressure throughout the system is uniform, but in
some places there are vacuum spots.
The concept of the vacuum system is quite different: the vapor
from the boiler is moving along the tubes, condensing and creating local vacuum spots. Unlike in a steam system, no air is sucked in through the air vents, so the radiators are still under a vacuum. When vapor gets into and heats some radiators, the temperature and vapor pressure in these radiators increases,
so less vapor is sucked in. Correspondingly, more vapor is sucked into other colder radiators so the heat distribution is naturally balanced by the system.
Some commercial vacuum systems are supposed to operate at lower pressure to avoid temperature fluctuations. In the seventies boilers were being replaced with multiple smaller boilers. So usually one boiler ran continuously,second boiler came on before morning and before late afternoon,third boiler came on for cold weather. LAOSH says that is wasteful strategy but building owners were please with results.
In this scenario, when the condensate pump's check valve starts to leak, the first fluid to back flow through the check valve is the condensate water that's in the pipe between the check valve and the vented receiver.
If the condensate pump doesn't start before the vacuum pulls all the water out of the pipe, then the next fluid the vacuum pulls past the check valve is air. This back flow of air pulls all the prime out of the condensate pump, so when it does start, there is no water in the volute and the impeller is spinning in air, so it doesn't pump any water.
A temporary fix for this problem is to change the check valve, but the problem will return when the check valve starts leaking again.
A permanent solution to this problem is to change the piping so there is always a water seal present.
This can be accomplished in any one of 3 ways:
1) Change the piping so you are filling the boiler feed tank FROM THE BOTTOM.
2) Install an internal submerged water outlet pipe inside the boiler feed tank. The open end should always be below the tank's lowest water level.
3) Revise the boiler feed tank's external inlet piping so it first drops down to the lowest level of the tank, then using a 90 elbow and a tee, pipe back up to the boiler feed tank's normal inlet connection. Now run a horizontal pipe from the remaining tapping on the tee to the tank's drain tapping.
Any one of these 3 arrangements will provide a permanent water seal, so when the check valve starts leaking again, the only fluid that will back flow will be water.
You may notice the condensate pump short cycling and come to the conclusion that the check valve is leaking again, but it now won't become air bound and stop pumping altogether.
Website: www.nashjenningspumps.com
The first step in solving any problem is TO IDENTIFY THE PROBLEM.
I can still raise the temperature in the system passed the saturation starting point without first "cooking the block" , but I won't see a zero gauge reading until I get 212°?
Don't need check valves or vacuum return lines in one pipe. Plug the vents and suck anywhere in supply. If you want to get fancy you can include closing king valve,sucking,opening king valve,firing in control sequence.
====================================
That simple recipe may work for ideal leak tight system but for existing 50+ year old single pipe system you'll get problems:
- the modified system would not heat up quicker - heavy steel piping have to be preheated before any heat get into radiators regardless if it's run in vacuum or at positive pressure.
- vacuum pump will catch a lot hot condensate from the system unless it's cool down completely.
Actually, I had tested such a lab pilot (3 radiators, copper lines, Propress fittings, some leaks in a boiler) - dropped the idea.
It would be more reasonable to add a small diameter vapor supply line to the top of each radiator and use original piping for condensate return and air evacuation via a vacuum
pump.
Adding vacuum lines to radiator has benefits. By serendipity (if you're lucky you don't have to be smart) I found that additional air can be removed from the system when vapor from boiler is pushing air into radiators and vacuum pump sucks air from air vents. When system cools, 25-26"Hg vacuum is achieved while vacuum pump switch is set to only 14-18"Hg. This can't be done in a closed single pipe vacuum system.
https://heatinghelp.com/systems-help-center/a-new-look-at-vacuum-heating/
Sorry about all the multiple posts. For some reason, my post was "waiting for approval", and still showed in the Leave a Comment box every time I checked in. I now see it got approved multiple times!
Never had that happen before, so not sure how that procedure works. I'll have to look more closely next time.
Website: www.nashjenningspumps.com
The first step in solving any problem is TO IDENTIFY THE PROBLEM.
I would think no longer needing to build pressure with the steam is where his massive savings are coming from.
"High pressure flows to low
pressure- always" -DH [some world
famous steam/hydronic guru]
The aforementioned vacuum system's primary [but not only] function addresses this. Of course, vacuum communicates all the way back to radiator valves be they fixed or thermostatically controlled.
But then there's the Other vacuum system, subatmospheric vacuum where the whole system goes negative including the boiler. The idea is to:
1) expand the steam
2) lower the boiling temperature of water
3) increase the latent heat content of that steam per unit of WEIGHT. [it takes up a lot more space so that there are fewer pounds of steam in a given radiator, this less total heat delivered]
This is the magic of Igor's system. It becomes easy to put a little heat into the system without a complex of equipment and active controllers.
The heating medium simultaneously becomes:
Cooler
Lighter
Faster
More heat per pound (not temperature!) but at a greater volume.
It's still critical to get and keep
air out since air will expand under vacuum too. This is why I believe Igor wants such a deep vacuum while the system is cool. And also why he introduced a small, simple vacuum pump to assure this critical feature is always met.
At that critical starting point, the pressure differential is generated solely by both the vast expansion of water to steam at the boiler and the equal and opposite localized vacuum created by the vast contraction of steam back into water. Think of a pushmepullyou.
The power required for air purging is removed and the thermal transfer is at its most efficient.
And, as Igor has pointed out, the room temperature itself sets up larger temperature differential at the radiator or convector that translates directly into a greater pressure differential wherever it's needed. No external controls necessary.
I might add, that I think some of the benefit is brought about by lowering the mass of the piping supply components. This allows for lower condensation-derived pressure differential within the piping and maximizing it at the radiators. The expansion effect at the radiator inlet also increases the steam's latent heat and dryness right at its point of use. We also see this effect in Gerry Gill's Improved Mini Tube steam heating system ( aka SelecTemp without the problematic unit heaters). Remarkably low fuel consumption is seen here too.
Igor's idea excels since the boiler doesn't have to fully commit to full temp and building a head of steam to force the preheating and air purging. A little dab of heat will do ya. But without a plethora of pumps and controllers.
@Pumpguy that's a good idea to feed the vented receiver from a low point. The check valves are well immersed as it is. But we haven't gotten to cutting and welding a threadolet in the bottom of the feed tank since we need a healthy size there owing to the duplex condensate unit's ability to run both pumps at the same time. That and access there stinks. And it still doesn't answer the question of "We can send a man to the moon but we can't make a check valve last more than two years!" Okay. That wasn't a question but you know what I mean.
I wish my writing was of such clarity as yours ... Thanks.
I'm sure the tank has a plugged drain tapping. Remove the plug and run a horizontal line out from this drain tapping to the run of one side of an appropriately size. Pipe the branch tapping of this tee up to the normal inlet connection on the vented boiler feed tank. Now pipe the remaining run tapping of this tee to the condensate pump discharge pipe.
Wallah! Permanent water seal, and no more air bound condensate pump when it discharges from a vacuum.
Website: www.nashjenningspumps.com
The first step in solving any problem is TO IDENTIFY THE PROBLEM.
My suggestion is mainly to eliminate air,not run in vacuum.Takes less work to move steam in an empty pipe.
Has anyone measured interior temperature in steam radiator? I suspect condensation occurs significantly below 212° because air is present.