One or two draft regulators?
bruce_21
Member Posts: 241
in Oil Heating
I went to a job where there are two oil burners (a bock HWH and a furnace) going into one chimney thru a tee in the breeching. Does both these burners need a draft regulator?
0
Comments
-
If both appliance call for a regulator then yes, and maybe one after the tee.
Best would be to check draft cold at chimney base and before each regulator, then check as each one fires, and both firing.There was an error rendering this rich post.
0 -
-
Are there conditions where you'd use multiple regulators?
Say one for each appliance, plus a third on the flue? Or would you double up at each appliance?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
I had a 22 story tall building with an 3.5 mil atmospheric boiler that not only required dual barometric dampers, but it also required me t install a restrictive orifice in the flue breaching of the boiler to slow the flow of flue gas down and give it a chance to exchange energy. Dropped the buildings fuel consumption by 40% just with that one effort alone. Dropped it an additional 30% when we base loaded the system and DHW loads with three 199 modcons. So, yes, there are situations where numerous dampers are required.
METhere was an error rendering this rich post.
1 -
Thanks for the help!0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements