Beckett Flame Retention Head
ppllgg
Member Posts: 69
in Oil Heating
I have a Burnham V-18 series (Dry Base) Boiler w/ Beckett AF burner
It has a F-6 head that I'm going to replace, I've read that with (Dry Base sys.'s) the head should have a (opional) heat shield. (It looks like a ring in my old manual that seems to be a separate part) Because what I have presently is a one piece F-6 head (stamping). It's been there over 10 yr.'s ( It doesn't show any sign of heat damage, it's just old. Are those heat shields still used & do I really need one ?? I've tried to search for one without success.
Frank
It has a F-6 head that I'm going to replace, I've read that with (Dry Base sys.'s) the head should have a (opional) heat shield. (It looks like a ring in my old manual that seems to be a separate part) Because what I have presently is a one piece F-6 head (stamping). It's been there over 10 yr.'s ( It doesn't show any sign of heat damage, it's just old. Are those heat shields still used & do I really need one ?? I've tried to search for one without success.
Frank
0
Comments
-
-
-
The head protector was used on brick chambers to protect from the higher chamber temperature. Not needed with non-brick type chambers.0
-
-
I appreciate your Knowledge & Help Bob Bona.
Thanks,
Frank0 -
If you are looking for longevity, consider a post purge for 2 minutes. You will need a clean-cut pump or solenoid oil valve on high pressure line and a newer primary control like the Beckett Genisys or Honeywell R7284. I have several new boilers with this setup and for the last 3 years I have returned to do maintenance and I'm almost afraid to change any adjustments... they look like the day I installed them. Nozzle, Electrodes, Burner head, NO CARBON BUILDUP ANYWHERE!!!
Edward Young Retired
After you make that expensive repair and you still have the same problem, What will you check next?
1 -
Ed is absolutely correct, I find that 15 seconds does almost as well.EdTheHeaterMan said:If you are looking for longevity, consider a post purge for 2 minutes. You will need a clean-cut pump or solenoid oil valve on high pressure line and a newer primary control like the Beckett Genisys or Honeywell R7284. I have several new boilers with this setup and for the last 3 years I have returned to do maintenance and I'm almost afraid to change any adjustments... they look like the day I installed them. Nozzle, Electrodes, Burner head, NO CARBON BUILDUP ANYWHERE!!!
To learn more about this professional, click here to visit their ad in Find A Contractor.0 -
My recollection is the V-1 Series of boilers were not dry base units but wet base boilers. They originated when Burnham purchased American Standard which made this boiler before it was renamed, I can't recall the A/S model #. The V-1 Series had a narrow opening on the diagonal in the front section for access to combustion area and usually had a target wall and blanket on the chamber floor. The earlier target walls were dry and had to be cut to install, the wet pack version made it easy. Not sure how you are going to get to the rear wall in an 8 section boiler. I don't recall Burnham making a dry base cast iron boiler. A/S did and they often had their hanging burner on it, boiler cleaned from the front. In a chimney application with a good draft I can see no reason to post purge more than 30 seconds.0
-
HAY GUYS, Can I get some HELP here in identifying my boiler ?... I found this Info. behind that inspect panel loc. at the Front/Top of of boiler. (Burnham Boiler- Mod. # WV 18 - 9A S/N 8899035 ), My problem is I order a Comb. Chamber kit for a Burham V-18 series boiler, & it doesn't seem to match up w/what I got here ! (Lynn - Comb. Chamb. kit # 1064 say's it's for a Burnham V - 18 series boiler. My Combustion Chamber is a perfect Cube. (18"X18"X18") Can I just line the (5) surfaces with Kaowool Board ??.. & If so, What thickness would you recommend? ...1/2", 3/4",1", 11/2"or the 2" K- Board ?? I'm Hoping to Get this together Sooon & Running !! ANY & ALL TIPS & HELP w/this would be GREATLY APPRECIATED !!
FRANK0 -
-
-
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 913 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements