System 2000 tea kettle?
Dave19
Member Posts: 28
in Oil Heating
Had a System 2000 today making what I can only describe as a surging sound. Within 20 seconds of the burner coming on the noise starts. Pressure was high but the expansion tank was good so I purged the boiler and zones because it sounded similar to an air noise. No luck, boiler did the same thing, turned on and noise came back in about 20 seconds. Pressure was high again so I released some water and the noise surged faster. Seemed to be the loudest right below where the flue connects to the boiler in the heat exchanger, or maybe that's just where you hear it best because it's open. Could this be a scale issue? I know these boilers are supposed to be treated but this is a First time customer with no service records so I have no idea the history of the boiler. Energy Kinetics tech support said they had never heard of such an issue and said they would call me back. I don't think they are going to, so any help is appreciated.
0
Comments
-
They'll call you back. There's a guy from EK on this forum that is fantastic with help/service.
Can you post a video, or audio of whats happening?
What was the temperature when you heard this noise?There was an error rendering this rich post.
0 -
Does the pressure gage surge in sync with the sound?
Does the noise get worse when you lower the pressure?
What happens to the pressure if you turn the make up water off? Does it drop to zero?
Could be a scale accumulation issue.
METhere was an error rendering this rich post.
0 -
What did the water that came out look like? Sounds like you need to clean the system water and treat it with an inhibitor.
There was an error rendering this rich post.
0 -
Brought in a second set of eyes, and he agreed this is a scale issue. And fyi energy kinetics called me this morning to say the same. They suggested furnox. Thanks for the help guys.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements