gravity hot water someone converted to steam, or tried to.

Options
cgdelzell
cgdelzell Member Posts: 22
Some plumber replaced a 100 year old gravity hot water boiler with a Weil-McClain steam boiler and tried to convert to steam. he does not know much about steam. 4" hot water mains reducing as they go around the house. no pressure switch, header drip on end of a horizontal tee with a concentric reducer. Hartford loop 4" below low water cut-off. Oh and the old boiler had nothing wrong with it.

Comments

  • JUGHNE
    JUGHNE Member Posts: 11,062
    Options
    How well does it work? Pictures would really be interesting.
  • Steamhead
    Steamhead Member Posts: 16,843
    Options
    I've seen a few of these conversions in Baltimore. If done right, they're fine. How long ago was this done?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • cgdelzell
    cgdelzell Member Posts: 22
    Options
    within last 6 months, no vents on radiators it they wanted 1 pipe steam. no control of temps in different rooms.
  • Steamhead
    Steamhead Member Posts: 16,843
    Options
    Can you take some pictures and post them?
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • cgdelzell
    cgdelzell Member Posts: 22
    Options
    no pictures until I get access again, buyers of house will give seller's contractor time to make it meet code.
    they did pull a permit.
    But no permits for plumbing and electric work that was done.
  • Danny Scully
    Danny Scully Member Posts: 1,425
    edited March 2016
    Options
    Any chance the guy saw big pipes and thought it was steam? :smiley: lol
  • cgdelzell
    cgdelzell Member Posts: 22
    Options
    nope, just stupid. he installed a bomb.
  • jumper
    jumper Member Posts: 2,260
    Options
    Don't see why it can't work. If plumber remembers to close off open tank somewhere high in the house. Otherwise venting is well taken care of, ha ha. Theoretically radiators are over sized so traps are redundant. With both HHW and steam the trick is air elimination. Picture a two pipe counterflow.....
  • cgdelzell
    cgdelzell Member Posts: 22
    Options
    Oh shucks, that's why it worked a little bit, forgot about tank in attic.
  • cgdelzell
    cgdelzell Member Posts: 22
    Options
    Don't see why it can't work. If plumber remembers to close off open tank somewhere high in the house. Otherwise venting is well taken care of, ha ha. Theoretically radiators are over sized so traps are redundant. With both HHW and steam the trick is air elimination. Picture a two pipe counterflow.....

    and no room control if steam enters from return main.
  • cgdelzell
    cgdelzell Member Posts: 22
    Options
    Have not been back to house, but the sale was delayed so the contractor could install pumps, prv fill valve, remove Hartford loop and pressure test system for 30 lb. system.
  • ChrisJ
    ChrisJ Member Posts: 15,706
    Options
    While everyone knows I'm always biased towards steam, if it's a hot water system isn't any WM steamer easily converted to hot water?
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • cgdelzell
    cgdelzell Member Posts: 22
    Options
    yes, same boiler. just replace steam water fill system with prv, add pressure tank, remove Hartford loop and add pump.
    Older Weil-McClain's could be used for gravity hot water.
  • cgdelzell
    cgdelzell Member Posts: 22
    Options
    You leave low water cutoff in place. Oh and add limit switch, and operator switch.