Reconnected radiator in one-pipe system
ADanemayer
Member Posts: 3
I recently reconnected a ~6 foot finned radiator in a back room of our second floor unit and have been getting inconsistent heat as well as water (heavy deposits) out the valve at the end, as well as water hammer. This unit had been disconnected over 6 years ago and is fed on it's own line from the boiler. After some preliminary searches online I boiled the valve in vinegar and also confirmed the pitch on the radiator but am still experiencing the same symptoms. I've been working my way through "We Got Steam Heat" and am questioning the feed pipe design that was put in place as well as the possible need for an adjustable valve due to the overall design of the single-pipe system heating this second floor unit. In addition, I have not been able to locate a main valve on either of the feeds leaving the boiler.
Can someone weigh in on whether or not the two-elbow feed (BackRoom_1.jpg) is appropriate, as well as whether or not the valve (BackRoom_2.jpg) should be replaced with something adjustable to help balance the system as a whole? I've included a diagram of the system (SecondFloor_Steam.jpg) and can provide more detail where required. Any help is appreciated as I have been trying to get this back room heated to alleviate some cold walls in the adjoining nursery. Thanks in advance!
Can someone weigh in on whether or not the two-elbow feed (BackRoom_1.jpg) is appropriate, as well as whether or not the valve (BackRoom_2.jpg) should be replaced with something adjustable to help balance the system as a whole? I've included a diagram of the system (SecondFloor_Steam.jpg) and can provide more detail where required. Any help is appreciated as I have been trying to get this back room heated to alleviate some cold walls in the adjoining nursery. Thanks in advance!
0
Comments
-
Pictures of boiler piping....and pics where this comes off the main would help.....are you sure everything is properly pitched? The way the piping is it looks like you really cannot get much pitch......whats the pipe size? I think i see a bushing between the 2 ells.....i would just put a regular radiator.....you may have to add more venting at the top of riser and a shut off valveASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
Make sure both the convector and that horizontal pipe are pitched right. What vent are you using now, convectors are happiest when they are vented slowly.
More pictures of the boiler and piping would help.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
The way that is piped you may have real trouble getting adequate pitch to drain -- two elbows like that almost guarantee that either the horizontal pipe run will pitch the wrong way, or the convector will.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
-
You need to hookup the convector as a two-pipe setup. There's been threads about it posted before.0
-
It's also covered in "The Lost Art of Steam Heating".Abracadabra said:You need to hookup the convector as a two-pipe setup. There's been threads about it posted before.
All Steamed Up, Inc.
Towson, MD, USA
Steam, Vapor & Hot-Water Heating Specialists
Oil & Gas Burner Service
Consulting0 -
What type radiators in the rest of the house ? If cast radiators look around for an replacement .. pipe and tube backboard should be piped with an return ... Pipe and tube baseboard in design needs its cover for convection ...
There was an error rendering this rich post.
0 -
Thank you all for the confirmation regarding the convection radiator. I had a suspicion that this was not piped correctly (the previous owner was a "self-taught professional" who left his mark in many ways) and will be looking to purchase a cast radiator in the next couple months to match the rest of the system.
As far as the original diagram of the piping, I realized that there is one feed out of the boiler that splits to the back room and then to the rest of the unit. Apologies for the inaccuracy there.
For now I am going to replace the cap where the first elbow sits and use a space heater until I can locate a replacement radiator. Anyone looking for a ~6 foot length of convection radiator?0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements