The pic below shows a job that i am correcting due to pipe size. I will be increasing pipe size from 3/4 to 1 1/4". Pipe size from boiler and indirect is 3/4...and boiler is piped incorrectly.There is a existing laars minitherm 160. I will be keeping the 4 way (1 1/4) "dumb" mixing valve with the zone valves and pump on the system side. I will be installing new indirect on priority and repiping boiler. The laars boiler recommends a bypass or a primary secondary setup. If i us the primary secondary setup would i have to use an extra pump on the boiler side of the 4way valve?Would this setup work? Any other suggestions will be appreciated thanks
ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company

Comments

  • Paul S_3
    Paul S_3 Member Posts: 1,280
    edited March 2016
    Or would this be a better setup? Primary secondary
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • hot_rod
    hot_rod Member Posts: 23,385
    A hydraulic separator would be another option. It would give you separation, air, dirt, and magnetic in one device.

    The 4 way without an actuator and control neither gives you boiler protection or accurate temperature mixing, it's just a guess as to where in needs to be set and adjusted. With a non-con you need some sort of boiler protection.

    Does the boiler show any signs of running too cold? Inspect the heat exchanger carefully, it may be on borrowed time.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Leon82
  • STEVEusaPA
    STEVEusaPA Member Posts: 6,505
    @hot rod Hey Bob, quick question, even though both circs have flow checks, does pointing them at each other have any potential maintenance/failure issues-long term? Just wondering

    There was an error rendering this rich post.

  • Paul S_3
    Paul S_3 Member Posts: 1,280
    Hot rod....i understand what you are saying....but would both my drawings work? I put in a quote for tekmar 360 with act motor setup.....the boiler does have signs of sustained flue gas condensation...all of the zones are lo temp radiant....and would a bypass or primary secondary help with this?
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • hot_rod
    hot_rod Member Posts: 23,385
    better? From an old PM Engineering article
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    kcopp
  • hot_rod
    hot_rod Member Posts: 23,385

    @hot rod Hey Bob, quick question, even though both circs have flow checks, does pointing them at each other have any potential maintenance/failure issues-long term? Just wondering


    I don't think so if only one runs at a time.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
  • Paul S_3
    Paul S_3 Member Posts: 1,280
    Yes...thanks hot rod....but i will have the indirect pump pumping towards the tank
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • hot_rod
    hot_rod Member Posts: 23,385
    Paul S said:

    Yes...thanks hot rod....but i will have the indirect pump pumping towards the tank

    In your drawing, I'm not sure you need 4 pumps? The primary loop circ and system circ are in series, the more the 4 way opens, the more you are moving to doubling head.

    Assure the boiler gets proper flow with that circ selection, I think the system pump should be enough for the radiant and loop it connects to.

    I'm still pushing for the sep :)

    I like the indirect on the primary side of the sep, or loop, as you have it. If you want both indirect and radiant circs on the secondary, a check would be wise to prevent flow potential thru a "off" radiant zone.

    There are a number of way to pipe this, I like a simple, multi-tasking component (sep) approach.

    If the indirect can handle the full boiler output, circs properly sized, there would be minimal temperature blending in the sep.
    Bob "hot rod" Rohr
    trainer for Caleffi NA
    Living the hydronic dream
    Ironman
  • Aaron_in_Maine
    Aaron_in_Maine Member Posts: 315
    Instead of a sep if you have small micro zones maybe a buffer tank as a sep to keep the boiler from short cycling. Don't know what you have just spit balling.

    There was an error rendering this rich post.

  • Paul S_3
    Paul S_3 Member Posts: 1,280
    Thank you guys much appreciate it ....im goin with the sep4