would this work
Paul S_3
Member Posts: 1,280
The pic below shows a job that i am correcting due to pipe size. I will be increasing pipe size from 3/4 to 1 1/4". Pipe size from boiler and indirect is 3/4...and boiler is piped incorrectly.There is a existing laars minitherm 160. I will be keeping the 4 way (1 1/4) "dumb" mixing valve with the zone valves and pump on the system side. I will be installing new indirect on priority and repiping boiler. The laars boiler recommends a bypass or a primary secondary setup. If i us the primary secondary setup would i have to use an extra pump on the boiler side of the 4way valve?Would this setup work? Any other suggestions will be appreciated thanks
ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
0
Comments
-
Or would this be a better setup? Primary secondaryASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
A hydraulic separator would be another option. It would give you separation, air, dirt, and magnetic in one device.
The 4 way without an actuator and control neither gives you boiler protection or accurate temperature mixing, it's just a guess as to where in needs to be set and adjusted. With a non-con you need some sort of boiler protection.
Does the boiler show any signs of running too cold? Inspect the heat exchanger carefully, it may be on borrowed time.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
@hot rod Hey Bob, quick question, even though both circs have flow checks, does pointing them at each other have any potential maintenance/failure issues-long term? Just wondering
There was an error rendering this rich post.
0 -
Hot rod....i understand what you are saying....but would both my drawings work? I put in a quote for tekmar 360 with act motor setup.....the boiler does have signs of sustained flue gas condensation...all of the zones are lo temp radiant....and would a bypass or primary secondary help with this?ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
better? From an old PM Engineering articleBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
STEVEusaPA said:
@hot rod Hey Bob, quick question, even though both circs have flow checks, does pointing them at each other have any potential maintenance/failure issues-long term? Just wondering
I don't think so if only one runs at a time.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Yes...thanks hot rod....but i will have the indirect pump pumping towards the tankASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
In your drawing, I'm not sure you need 4 pumps? The primary loop circ and system circ are in series, the more the 4 way opens, the more you are moving to doubling head.Paul S said:Yes...thanks hot rod....but i will have the indirect pump pumping towards the tank
Assure the boiler gets proper flow with that circ selection, I think the system pump should be enough for the radiant and loop it connects to.
I'm still pushing for the sep
I like the indirect on the primary side of the sep, or loop, as you have it. If you want both indirect and radiant circs on the secondary, a check would be wise to prevent flow potential thru a "off" radiant zone.
There are a number of way to pipe this, I like a simple, multi-tasking component (sep) approach.
If the indirect can handle the full boiler output, circs properly sized, there would be minimal temperature blending in the sep.
Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Instead of a sep if you have small micro zones maybe a buffer tank as a sep to keep the boiler from short cycling. Don't know what you have just spit balling.
There was an error rendering this rich post.
0 -
Thank you guys much appreciate it ....im goin with the sep4ASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
Who tried to read the backwards writing at the top of the page.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements