Steam boiler repipe in Jersey City NJ

Options
EzzyT
EzzyT Member Posts: 1,295
We repiped this boiler with a 4" drop header and the hydronic loop piping going to the indirect tank as a preheated tank for the regular hot water heater. Indirect tank started to leak after we repiped it properly. The only thing I could come up with that prevented it from leaking before or masked the leak was all the mud and dirt sitting at the bottom of tank and once we drained it and repiped it that exposed the leak. We ended up ripping out the indirect tank and the old water water heater and upgraded the water heater from a 40 gallon to a 75 gallon with a mixing valve.
The hydronic loop piping is staying for the future baseboard heat that's going into the basement.
E-Travis Mechanical LLC
Etravismechanical@gmail.com
201-887-8856
LionA29aircooled81

Comments

  • EzzyT
    EzzyT Member Posts: 1,295
    Options
    Exactly.
    Thanks Brian
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
  • LionA29
    LionA29 Member Posts: 255
    Options
    Great Job @EzzyT!
  • Paul S_3
    Paul S_3 Member Posts: 1,261
    Options
    Nice job EZZY! ....beautiful work
    ASM Mechanical Company
    Located in Staten Island NY
    Servicing all 5 boroughs of NYC.
    347-692-4777
    ASMMECHANICALCORP@GMAIL.COM
    ASMHVACNYC.COM
    https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company
  • EzzyT
    EzzyT Member Posts: 1,295
    Options
    Thanks Lionel and Paul
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
  • DanHolohan
    DanHolohan Member, Moderator, Administrator Posts: 16,528
    Options
    That's beautiful, Ezzy. Thanks for sharing your art with us.
    Retired and loving it.
  • EzzyT
    EzzyT Member Posts: 1,295
    Options
    Thanks Dan
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
  • aircooled81
    aircooled81 Member Posts: 205
    Options
    Thank you for posting those pictures, outstanding craftsman ship.
  • Dave0176
    Dave0176 Member Posts: 1,177
    Options
    Nice Ez... No before pics?? Is that an EG-50 or 55??
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

    I cannot force people to spend money, I can only suggest how to spend it wisely.......
  • EzzyT
    EzzyT Member Posts: 1,295
    Options
    EG-50
    Before pictures
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
  • Dave0176
    Dave0176 Member Posts: 1,177
    Options
    Wow Just........ Wow, look at those little pee shooters.......
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

    I cannot force people to spend money, I can only suggest how to spend it wisely.......
  • ChrisJ
    ChrisJ Member Posts: 15,708
    Options
    @Dave0176

    Was easy to tell it was a 50 by the drafthood.
    EG*5 boilers have full size. The EG*0 have reduced with the round bottom.

    Unless that's a recent change, but judging by how my EG-40 worked with the 45 hood I doubt it.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • ChrisJ
    ChrisJ Member Posts: 15,708
    Options
    @EzzyT Another perfect install. Excellent work!
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • ChrisJ
    ChrisJ Member Posts: 15,708
    Options
    Hey, what's with that gas stove!!!!!!
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • Dave0176
    Dave0176 Member Posts: 1,177
    Options
    ChrisJ said:

    @Dave0176

    Was easy to tell it was a 50 by the drafthood.
    EG*5 boilers have full size. The EG*0 have reduced with the round bottom.

    Unless that's a recent change, but judging by how my EG-40 worked with the 45 hood I doubt it.

    Thanks Chris, I actually didn't even look at the draft hood.
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

    I cannot force people to spend money, I can only suggest how to spend it wisely.......
  • EzzyT
    EzzyT Member Posts: 1,295
    Options
    Thanks Dave and Chris.
    The stove was used by the previous owner. It still works and works great.
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
  • EzzyT
    EzzyT Member Posts: 1,295
    Options
    thanks @aircooled81
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
    happydave
  • Jack M
    Jack M Member Posts: 229
    edited February 2016
    Options
    Is that a series 100 Bell & Gossett circulating pump (with the bronze sleeve)? What model? Sweet job squeezing that in there.
  • EzzyT
    EzzyT Member Posts: 1,295
    Options
    Yes that is a B&G 100 AB bronze 1/12 HP pump.
    Thanks
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
  • ChrisJ
    ChrisJ Member Posts: 15,708
    Options
    Wow,

    Why would anyone use one of those typical Taco circulatory when you can have one of those!

    I want one and I don't even have a hot water loop! I want to hang it on the Christmas tree or something.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
    vaporvacLionA29njtommyaircooled81
  • Fred
    Fred Member Posts: 8,542
    Options
    Beautiful, Ezzy
  • LionA29
    LionA29 Member Posts: 255
    edited February 2016
    Options
    Easy there @Hatterasguy
    @ChrisJ will need a Baycrane to hoist that piece.
  • EzzyT
    EzzyT Member Posts: 1,295
    Options
    Thanks @Fred
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
  • Jack M
    Jack M Member Posts: 229
    edited March 2016
    Options
    Looks like a lot of effort went into supporting the suction and discharge pipes on both sides of the pump. Don't always see that. Did the black metal bracket supporting the power pack come with the B&G 100 (AB bronze 1/12 HP) or is that a separate item?






    SWEI
  • EzzyT
    EzzyT Member Posts: 1,295
    Options
    Not to difficult installing the supports for the pump and piping.
    We either use a coated riser clamp or uni-strut as the support for the pump mortor
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
    SWEI
  • SWEI
    SWEI Member Posts: 7,356
    Options
    The hi-lighting is actually in the wrong place there. Read carefully...
  • Jack M
    Jack M Member Posts: 229
    edited March 2016
    Options
    SWEI said:

    The hi-lighting is actually in the wrong place there. Read carefully...

    Thanks SWEI, I see it now (little slow). The instruction say don't support the power pack.
    I have heard that these pumps can last forever if you keep them oiled. Sometimes you will hear them start to vibrate and that is a sign that the "mounts" need to be replaced. Oddly, replacement impellers are plastic. I would have guessed otherwise.
  • SWEI
    SWEI Member Posts: 7,356
    Options
    I'm not the only one who killed a 3-piece pump before I learned that...
  • Abracadabra
    Abracadabra Member Posts: 1,948
    Options
    Jack M said:

    SWEI said:

    The hi-lighting is actually in the wrong place there. Read carefully...

    Thanks SWEI, I see it now (little slow). The instruction say don't support the power pack.
    I have heard that these pumps can last forever if you keep them oiled. Sometimes you will hear them start to vibrate and that is a sign that the "mounts" need to be replaced. Oddly, replacement impellers are plastic. I would have guessed otherwise.
    There's brass ones too