flue pipe deteriorating
Paul S_3
Paul S_3 Member Posts: 1,297
what would cause this 2 condensing water heaters with the flue pipe deteriorating...only 2 years old....performed combustion analysis all ok....the manual says use pvc and/or stainless....I think the flue is the wrong type?
ASM Mechanical Company
Located in Staten Island NY
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
  • Ironman
    Ironman Member Posts: 7,904
    I don't understand why they started with PVC and then transitioned to stainless. If PVC is good enough close to the burner, then it would be good enough farther away.
    Check your firing rate on each burner to confirm it's what it's rated for.
    Bob Boan
  • Steve Minnich
    Steve Minnich Member Posts: 2,876
    Look at the detail of the flue gas path. I can't believe that's how the manufacturer calls for that, especially the use of the Y PVC fitting?
    Steve Minnich
  • Henry
    Henry Member Posts: 998
    It is not listed for a condensing boiler application. S636 is for condensing boilers.
  • Paul S_3
    The stainless pipe is not listed for condensing boilers?
    347-692-4777
    ASMHVACNYC.COM
  • njtommy
    njtommy Member Posts: 1,101
    I'm sure your not supposed to use the Y style T. That seems silly to me.
  • Steve Minnich
    Or have a 45 looking down any flue?
    Steve Minnich