There is a limit...

Jamie Hall
Jamie Hall Member Posts: 24,853
-20 F this morning, with about a 10 mph wind. For southern New England, that's chilly. It turns out that that's what Cedric can manage -- 86 degree temperature difference, but the poor old boy can't raise it any more. It did raise it from the 3 degree night setback, but can't get over that.

Nice to know where the limit is, anyway!

Anybody else?
Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
«1

Comments

  • KC_Jones
    KC_Jones Member Posts: 5,840
    I made it to 4 ounces and had my low fire kick in today 7° OAT which is my design temp. No trouble maintaining 70, but as far as my radiation goes I was running full out this morning coming back from 3 degree setback. My radiation is 63600 BTU and my calculated heat loss is ~60k BTU. Running good now that we are up to 18.
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • Brewbeer
    Brewbeer Member Posts: 616
    New baseboard system, 130 supply water temps. Got down to -13 last night (2 out now). 70 inside now, recovered nicely from a 3 degree setback.
    Hydronics inspired homeowner with self-designed high efficiency low temperature baseboard system and professionally installed mod-con boiler with indirect DHW. My system design thread: http://forum.heatinghelp.com/discussion/154385
    System Photo: https://us.v-cdn.net/5021738/uploads/FileUpload/79/451e1f19a1e5b345e0951fbe1ff6ca.jpg
    njtommykcopp
  • sunlight33
    sunlight33 Member Posts: 378
    I set the maximum modulation on Vitoden 200 to 65%, it had absolutely no problem with -9 last night, as a matter of fact I think it should be fine even at 50-55%.
  • Fred
    Fred Member Posts: 8,542
    No issues here with -5 and a slight wind. Last winter I reached my max at -20 with a wind chill of -40. At that temp, I'm not sure I could have recovered from any set back.
  • Aaron_in_Maine
    Aaron_in_Maine Member Posts: 315
    Mine won't keep up below 0 degrees because of my own fault I took the heat out on the second floor when we didn't use it. Now we use one bedroom but I didn't put the heat back we just leave the door open keeps it around 64-66. I bought my wife a electric blanket instead when we moved our bedroom up there. My thermostat is set to 68 all the time but when it is below 0 the thermostat won't get above 66.

    There was an error rendering this rich post.

  • njtommy
    njtommy Member Posts: 1,105
    Hydro air had no problems keeping up last night. 0-5 degrees last night. Was going to try and dial in my max supply water temp this am, but had to go to work. Instead.
  • ChrisJ
    ChrisJ Member Posts: 16,315
    edited February 2016
    -5F with winds and as usual the EG-40 did just fine.
    Had no problem maintaining 73F and even recovered from a setback. Peak pressure during the recovery was 0.75"WC.


    Chances are I won't know my systems limits unless we see -30F here.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Jamie Hall
    Jamie Hall Member Posts: 24,853
    For what it's worth, some miscellaneous playing with numbers showed me that first, my system is limited by the installed radiation, not the boiler. Second, the boiler is uncommonly well matched to the radiation (it does shut off on pressure -- but it takes a run of at least 45 minutes to do it) (thank you, @Charlie from wmass and third, the gross efficiency of the system (BTU in from oil burned to heat loss from the building) is around 84% -- which for a non-mod/con system isn't too shabby (thank you again, @Charlie from wmass !).
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • ChrisJ
    ChrisJ Member Posts: 16,315

    For what it's worth, some miscellaneous playing with numbers showed me that first, my system is limited by the installed radiation, not the boiler. Second, the boiler is uncommonly well matched to the radiation (it does shut off on pressure -- but it takes a run of at least 45 minutes to do it) (thank you, @Charlie from wmass and third, the gross efficiency of the system (BTU in from oil burned to heat loss from the building) is around 84% -- which for a non-mod/con system isn't too shabby (thank you again, @Charlie from wmass !).

    They all are, that's what we keep saying regarding oversizing a boiler. A boiler that is 33% larger than the connected radiation will provide no more heating than one that is 0% oversized.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Jamie Hall
    Jamie Hall Member Posts: 24,853
    Actually, a bit of a fudge, there, @Hatterasguy . I didn't determine the building heat loss directly (that would be an interesting exercise, though!). What I did was note that the system, running essentially continuously (a minute off every 15 minutes or so on pressure) was able to hold the interior temperature constant, but not change it. The shaky assumption then is that installed radiation really is producing that 240 BTU/hr per square foot that we like to talk about! And I know what that is. That gives me the heat loss from the building.

    Accurate? Hardly. But I doubt that it's much worse than anything else!

    Infiltration -- oh yes indeed. I am quite convinced that it is a very significant part of the heat loss. This was on a not particularly breezy morning, but 50% may be low even so. I'm not at all sure that there is a good way to determine it, at least on a somewhat normal house -- there are simply too many variables. A new build, with excellent workmanship throughout (yeah, right) -- yes, and it would be tight enough that a controlled outside air exchange would be required (through a sensible heat heat exchanger, of course). But an ordinary house?

    Maybe I should sit down and take the time to figure out what the calculated heat loss for this monster should be, and compare that!
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • njtommy
    njtommy Member Posts: 1,105
    33%? I think your number needs to go up 17% lol
  • BobC
    BobC Member Posts: 5,502
    @Jamie Hall I think you are measuring the heat loss of that building accurately under real world conditions.

    If the boiler is running constantly and everything is heated fully across you know whats going in to the building and you know the point at which you can no longer raise the temperature of the building.

    That seems to be a pretty accurate measure of heat loss to me.

    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • ChrisJ
    ChrisJ Member Posts: 16,315
    What about heat from the boiler and pooping? Flue pipe too?

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • BobC
    BobC Member Posts: 5,502
    If his cellar is anything like mine it has little effect. It was -9F this morning and my cellar was 44F, large expanses of exposed foundation.

    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • ChrisJ
    ChrisJ Member Posts: 16,315
    Wow piping not pooping. Using my phone tonight and not used to it. Still

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Steamhead
    Steamhead Member Posts: 17,380
    ChrisJ said:

    Wow piping not pooping. Using my phone tonight and not used to it. Still

    http://www.damnyouautocorrect.com/

    >:)
    All Steamed Up, Inc.
    Towson, MD, USA
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Consulting
  • KC_Jones
    KC_Jones Member Posts: 5,840
    ChrisJ said:

    Wow piping not pooping. Using my phone tonight and not used to it. Still

    You wouldn't have that issue on an iPhone. lmao
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
  • Canucker
    Canucker Member Posts: 722
    To be fair to @ChrisJ we do bang on about having an accurate heatloss and after looking at his steam set up he does take his heating to the extreme ;)
    You can have it good, fast or cheap. Pick two
  • Brewbeer
    Brewbeer Member Posts: 616
    edited February 2016
    To test limits, I set the boiler (WHN 55) to 60% maximum fire yesterday to see how it did over the night when temps dipped to -10. A 60% output (~29K BTU), the boiler was keeping up with demand, although with all three zones running this morning the boiler supply temp was still a few degrees below the boiler's 130F maximum supply set point, and set-back recovery was taking noticeably longer.

    Three lessons learned from this cold snap:
    1) the heat loss calculated for the house (32K @ 0F, or 36K @ -10F) is too high (20% over estimation?).
    2) the ODR can be further adjusted to decrease the supply water temps (from 130F @ 0F to 130F at -10F).
    3) the boiler can be limited to a maximum fire of 60% in SH mode.
    Hydronics inspired homeowner with self-designed high efficiency low temperature baseboard system and professionally installed mod-con boiler with indirect DHW. My system design thread: http://forum.heatinghelp.com/discussion/154385
    System Photo: https://us.v-cdn.net/5021738/uploads/FileUpload/79/451e1f19a1e5b345e0951fbe1ff6ca.jpg
  • hvacfreak2
    hvacfreak2 Member Posts: 500
    Knock on wood I have all the heat I have asked for. I really appreciate the help that everyone on here has given me. I am heating 431 sq.ft. with a Megasteam 396 and it hasn't missed a beat. I was really worried about the sizing especially with the low pressure I was seeing when I first fired up. It has really been easy on the oil consumption as well.
    hvacfreak

    Mechanical Enthusiast

    Burnham MST 396 , 60 oz gauge , Tigerloop , Firomatic Check Valve , Mcdonnell Miller 67 lwco , Danfoss RA2k TRV's

    Easyio FG20 Controller

    vaporvacSWEI
  • bmwpowere36m3
    bmwpowere36m3 Member Posts: 512
    Brewbeer said:

    To test limits, I set the boiler (WHN 55) to 60% maximum fire yesterday to see how it did over the night when temps dipped to -10. A 60% output (~29K BTU), the boiler was keeping up with demand, although with all three zones running this morning the boiler supply temp was still a few degrees below the boiler's 130F maximum supply set point, and set-back recovery was taking noticeably longer.

    Three lessons learned from this cold snap:
    1) the heat loss calculated for the house (32K @ 0F, or 36K @ -10F) is too high (20% over estimation?).
    2) the ODR can be further adjusted to decrease the supply water temps (from 130F @ 0F to 130F at -10F).
    3) the boiler can be limited to a maximum fire of 60% in SH mode.

    Yup, mine's been throttled to 35%... but it did lose a couple degrees Saturday night into sunday.
  • ChrisJ
    ChrisJ Member Posts: 16,315
    edited February 2016

    Knock on wood I have all the heat I have asked for. I really appreciate the help that everyone on here has given me. I am heating 431 sq.ft. with a Megasteam 396 and it hasn't missed a beat. I was really worried about the sizing especially with the low pressure I was seeing when I first fired up. It has really been easy on the oil consumption as well.

    431sqft?
    Ah nm 431 sqft of radiation.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • hvacfreak2
    hvacfreak2 Member Posts: 500
    431 , is it a secret code like 420 ?
    hvacfreak

    Mechanical Enthusiast

    Burnham MST 396 , 60 oz gauge , Tigerloop , Firomatic Check Valve , Mcdonnell Miller 67 lwco , Danfoss RA2k TRV's

    Easyio FG20 Controller

  • hvacfreak2
    hvacfreak2 Member Posts: 500
    lol.

    I was sitting here at the computer the other day and thought " man I wish there was a small radiator here near my feet ". I looked down at the lan cable that goes down to the basement through an existing hole. And remembered the capped take-off on the main near the hole. May be time to make it 440 ( I'm a Mopar guy anyway ).
    hvacfreak

    Mechanical Enthusiast

    Burnham MST 396 , 60 oz gauge , Tigerloop , Firomatic Check Valve , Mcdonnell Miller 67 lwco , Danfoss RA2k TRV's

    Easyio FG20 Controller

  • Jamie Hall
    Jamie Hall Member Posts: 24,853
    Add another 14 and make it a big block...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • hvacfreak2
    hvacfreak2 Member Posts: 500

    Subtract 5 for the finest Chrysler engine ever built.

    From a performance standpoint , no question. From an interesting , hobbyist perspective that goes to the first generation. Good grief I can't get started on this , lol.

    Steam traps , I picked up some brand new DB and Mepco to replace my main vents. It got cold so they are just sitting here , lol.

    hvacfreak

    Mechanical Enthusiast

    Burnham MST 396 , 60 oz gauge , Tigerloop , Firomatic Check Valve , Mcdonnell Miller 67 lwco , Danfoss RA2k TRV's

    Easyio FG20 Controller

  • Jamie Hall
    Jamie Hall Member Posts: 24,853
    Actually, just to throw a bit of a monkey wrench at this -- my favourite engine to play with was the 401 Buick nailhead (not the successor 400!). You could get a lot out of one of those with only a little effort. Of course, that assumes you could keep oil in it... the valve cover gaskets leaked like sieves...
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • ChrisJ
    ChrisJ Member Posts: 16,315
    The only old car engine I've worked on and know quite a bit about is a Ford model A.

    My dream engine would be any Harry Miller inline 8 or V16 but I've got a better chance of seeing god.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Fred
    Fred Member Posts: 8,542
    The Chrysler 383 and 440 would be my favorites. They ran forever if you took care of them.
  • ChrisJ
    ChrisJ Member Posts: 16,315
    Fred said:

    The Chrysler 383 and 440 would be my favorites. They ran forever if you took care of them.

    I see quotes like this often from people but it often confuses me being these engines are from the days when you either junked the car or rebuilt the engine at 100,000 miles.

    Being we often see 200,300 even 400,000 out of gas engines these days and from the 1980s-1990s I'm a bit surprised any 1950s-1960s engine would be described as "ran forever".


    I'm sure I just threw water on a grease fire, but, that's ok. It's Jamie's thread. :p

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Fred
    Fred Member Posts: 8,542
    @ChrisJ , they usually needed a valve job at 100K but they were simple to work on and I use to take the heads off, on a Friday night, run them to an auto machine shop on Saturday morning, pick them up on Saturday afternoon after the valve were ground, maybe a couple replaced and put the car back together on Sunday, ready for work on Monday. Carbs were a somewhat weak point too but you could take them off, go get a $30.00 rebuilt one, trade your core in and put in on in an hour or so. Of course, I'm sure everyone who ever owned a Chrysler (50's or 60's) remembers how the inside of the distributors would get damp, on rainy days and the car wouldn't start. OK, I take it back. Maybe they aren't my favorite, just fond memories. :)
  • ChrisJ
    ChrisJ Member Posts: 16,315
    IMO carbs are a big reason engines weren't lasting.
    Richer mixtures meant oil didn't work as well or last as long.

    Put fuel injection in, run engines hotter and use modern oil and I think you'll see very similar results to more modern engines.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Fred
    Fred Member Posts: 8,542
    The oils weren't as refined and didn't do as good a job lubricating back then. Engine tolerances weren't nearly what they are today, Gas quality wasn't what it is today. Lots of things affected the life of an engine. Carbs vs Fuel injection played a part also. Plus the only thing that adjusted the fuel/air mixture was the gas pedal and a crude butterfly choke. Today's computer mixed air/gas was a huge improvement and much more effecient. They were easy to work on though.
  • ChrisJ
    ChrisJ Member Posts: 16,315
    Fred said:

    The oils weren't as refined and didn't do as good a job lubricating back then. Engine tolerances weren't nearly what they are today, Gas quality wasn't what it is today. Lots of things affected the life of an engine. Carbs vs Fuel injection played a part also. Plus the only thing that adjusted the fuel/air mixture was the gas pedal and a crude butterfly choke. Today's computer mixed air/gas was a huge improvement and much more effecient. They were easy to work on though.

    Everything that was easy to work on is everything you never have to touch anymore so it's kind of moot.

    Modern engines have no plugs, no rotor, no points and no carb to work on.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Fred
    Fred Member Posts: 8,542
    Everything that was easy to work on is everything you never have to touch anymore so it's kind of moot.

    Modern engines have no plugs, no rotor, no points and no carb to work on.

    Agreed. But when a computer controlled device fails, you pay through the nose !
  • KC_Jones
    KC_Jones Member Posts: 5,840
    "Modern engines have no plugs"
    Huh? So does magic ignite the air fuel ratio?
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
    njtommy
  • ChrisJ
    ChrisJ Member Posts: 16,315
    KC_Jones said:

    "Modern engines have no plugs"
    Huh? So does magic ignite the air fuel ratio?

    Diesels. :)

    I meant wires, not plugs.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Fred
    Fred Member Posts: 8,542
    As best I know they have plugs that will last 100K miles. My Hummer is diesel, glow plugs
  • ChrisJ
    ChrisJ Member Posts: 16,315
    Yeah,
    What were plugs good for in 1960, 10,000 miles?

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Fred
    Fred Member Posts: 8,542
    edited February 2016
    ChrisJ said:

    Yeah,
    What were plugs good for in 1960, 10,000 miles?

    Yes! The problem with the 100K plugs is they weld to the heads in tht time and then they usually break off when you try to replace them. Then you end up pulling the heads anyway but at least that's at 100K