Got a call for poor heating of certain radiators, river sounds, marballs sounds spitting air vents, water hammer etc.

I went to the basement and found this concoction....... The main needed to be moved to make way for the basement being converted into a garage to clear the new garage door. The main starts as 2-1/2, he reduced down to 2" which is ok being only three remaining runouts then reduced at that 180 point back to the boiler to 1" then back up to 1-1/2 for the dry return. Can't make this stuff up.

I guess most plumbers really know nothing more then hot water heating. Lol