Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Converting from steam to hot water heat

Options
2»

Comments

  • hboogz
    hboogz Member Posts: 113
    Options
    @Charlie from wmass If I use a pipe how would that technically be configured ?

    Find a tee on the main, branch off of it, run your new section of pipe, then drop to below water line and tie into wet return. Drill and Tap vent hole in the section where i want the pipe to act as a radiator ?
  • Charlie from wmass
    Charlie from wmass Member Posts: 4,322
    Options
    How much heat do you need?
    Cost is what you spend , value is what you get.

    cell # 413-841-6726
    https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating
  • hboogz
    hboogz Member Posts: 113
    Options
    As an example i would say to heat an open space of say 600sq ft .
  • ChrisJ
    ChrisJ Member Posts: 15,677
    edited December 2016
    Options
    And what's the heatloss of that 600sqft?

    If there's no exterior walls and the ceiling is below a conditioned space it could in theory be close to 0 while if all four walls are exterior and the ceiling is exterior it could be quite high depending on wall construction, insulation etc.
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • hboogz
    hboogz Member Posts: 113
    Options
    @ChrisJ In my application, i would consider it in a finished basement space that has, what i would imagine is the basic R15 pink fiberglass batts on a masonry house. 3 small windows. nothing crazy.
  • SWEI
    SWEI Member Posts: 7,356
    Options
    All kinds of options there. A run of pipe (perhaps 2-3 in parallel) spanning the length of the space with reflective insulation above could work wonders.
  • hboogz
    hboogz Member Posts: 113
    Options
    Gotcha. Am I drilling and tapping for a vent ?
  • Charlie from wmass
    Charlie from wmass Member Posts: 4,322
    Options
    For one pipe systems yes. For 2 pipe no. Get a trap then.
    Cost is what you spend , value is what you get.

    cell # 413-841-6726