Munchkins- Insider tips
GW
Member Posts: 4,832
in Gas Heating
I updated some of my notes on the M80-M140 series, we have a few loyal customers with these units (you know, phone notes, computer notes, field notes).
For the 925 controller, #13 allows for a post purge on the boiler pump. Factory setting is ZERO (no purge), do you Munchkin experts move these to one at all? ONE may be good to move the heat?
#18 is the stepped modulation upon startup on the heating mode. Factory is ONE meaning it’s on. ZERO means it’s off, which means it would go direct to hi fire. Do you ever go to high fire off the bat?
I lost track of when they stopped making the M series. i bet there are many thousands within an hours drive
Thanks, and please share more insider tips.
For the 925 controller, #13 allows for a post purge on the boiler pump. Factory setting is ZERO (no purge), do you Munchkin experts move these to one at all? ONE may be good to move the heat?
#18 is the stepped modulation upon startup on the heating mode. Factory is ONE meaning it’s on. ZERO means it’s off, which means it would go direct to hi fire. Do you ever go to high fire off the bat?
I lost track of when they stopped making the M series. i bet there are many thousands within an hours drive
Thanks, and please share more insider tips.
1
Comments
-
Two thumbs up.... good stuff!0
-
-
One thing I remember was that the way the air intake was above the inducer would drip on to the motor and short it out. This was especially if there was cross contamination.
Suggestion was to for a small piece of metal to divert that away to the side.
I used this w/ a customer that went through 3 motors in 4 years. (ME shared that one)0 -
Ok good one, yet I'll need to visit one to see what you mean.
I thought the intake was a simple hole in the back of the munchkin.0 -
This was on a T-50 and/or T80.0
-
Do you have this 50 pager? Sent out 7/3/08. I have some that wholesalers put together also.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
I could use that one Hot Rod. Could you email it to me?
I just condemned one yesterday but not much troubleshooting necessary.Steve Minnich0 -
Me too, Bob, if I can get a copy.0
-
I sent a few to Stephen as a Dropbox link, if they arrived Ok I'll pass them along.
e-mail me your addressBob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
gary@wilsonph.com thanks, looking forward to it0
-
I have a ton of tips on Munchkin from my Troubleshooting Manual that I wrote several years ago. I do not want to spoil the fun so I will hold off on sharing them. In fact we just went through my manual this week in the Mod/Con class I ran. That along with several others on Mod/Cons I have written. I got a lot of my info from Brian French, John Sawyer, Jeff Cook and Chuck Shaw all who worked at HTP.
I would love a copy from you Hot Rod just to compare with my information.0 -
Just opened it, HR. Thank you.Steve Minnich0
-
-
8/25/15 Check the black molex plug; the outside wires (brown and blue) should read 24-27 volts DC. If you check the same wires at the circuit board, they should read 24-27 volts AC.
Incoming gas pressure should be 8-10" wc, outlet side should be -.01 wc
Check voltage at the flame probe, from probe to ground - you don't need to disconnect the wires. There should be 42-44 volts; if less than 38 volts, upgrade to the 925 board (black transformer).
Check rectification by pressing and holding S4, continue pressing S4 to get to d7 which will tell you how many µamps (micro amps) coming from the flame probe. The range should be 3 - 4½ µamps.
Also, check the voltage readings at the molex plug connected to the fan, the one with 4 wires. You should have 24-40 VDC at the red and blue connections.
8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab1 -
Hey, Hot Rod: Me too, please! berkeleyradiant@gmail.com8.33 lbs./gal. x 60 min./hr. x 20°ΔT = 10,000 BTU's/hour
Two btu per sq ft for degree difference for a slab0 -
Had a call yesterday from a customer with a 140m. Wanted too know if I was a munchkin "expert ". I asked what the trouble was. It won't run he said. I asked what was the error code. he said there is none. I asked if the tstat was set high enough. A pause and then it's running now. I guess I am a expert but would also like to have that trouble shooting book. Hot Rod. jf.simmons@verizon.net3
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements