  • andrewco
    andrewco Member Posts: 104
    Diagrams not included before
  • SWEI
    SWEI Member Posts: 7,356
    Need to see existing wiring to those two thermostats, especially where they (or their connected appliances) get their low voltage power. You'd be safest with an interposing relay there.
  • andrewco
    andrewco Member Posts: 104
    SWEI said:

    Need to see existing wiring to those two thermostats, especially where they (or their connected appliances) get their low voltage power. You'd be safest with an interposing relay there.

    Thermostat 1) controls the 5kW heater. This is the biggie. It's a NEST using 3 wires (using W1, C & Rh). Using previous guidence I would be breaking Rh with the relay

    Thermostat 2) controls the floor heat max draw 1000w but I've noticed it being much less than that. It's a 4 wire lv thermostat.
  • SWEI
    SWEI Member Posts: 7,356
    Where do those thermostats get their 24 VAC power?
  • andrewco
    andrewco Member Posts: 104
    The nest gets it from the RC840T on the C terminal I believe.

    The stepwarmfloor (floor heat) I'm still trying to figure that out. It's a 4 wire thermostat.
  • SWEI
    SWEI Member Posts: 7,356
    The safest route would be a DPST relay with its own power source.
  • andrewco
    andrewco Member Posts: 104
    ....and control that DPST relay from the current switch I assume?
  • SWEI
    SWEI Member Posts: 7,356
    Yes, the current switch would activate the DPST relay coil.
  • ratio
    ratio Member Posts: 3,777
    There might be an issue with that. The diagram you posted up-thread shows the aube relay as having 1.2 VA of power available, 40mA of which is committed to the coil of the relay. The math works out to a surplus of 10mA (unless I screwed it it, haven't done this since skool...), which might not be enough to draw in another relay. Also of concern is the inrush current, which can be an order of magnitude, or more, higher than the listed holding current.

    Of course, the easiest way to see if it will work is to try it!

    wyo
  • andrewco
    andrewco Member Posts: 104
    aube relay is spoken for. That's the one that controls the 24v thermostat (nest) via the 5kW garage heater. SWEI is suggesting establishing another relay specifically for the purpose of being able to control TWO individual thermostat's call for heat.
  • ratio
    ratio Member Posts: 3,777
    Right, but what powers the new relay? The aube internal power supply might not be stout enough to draw in another relay. (Also some concern re powering the Nest, I have zero experience with 'em, I worry about things I don't know about.) Powering the new relay off of the blue & red would mitigate that.
  • SWEI
    SWEI Member Posts: 7,356
    Lacking detailed info on the existing transformers and their loads, I was suggesting either a self-powered relay or a new transformer for the current switch & relay.
  • andrewco
    andrewco Member Posts: 104
    edited February 2016
    Sorry - I'm not going to use the existing transformers to power a new relay since all the secondary power is spoken for. As SWEI suggested, I would look at powering the new DPST with a separate power source (most likely the 240v circuit)
  • andrewco
    andrewco Member Posts: 104
    Just a quick update on this project. I've got all the controls in place and it's working great. I'd like to add a kwh meter to the EVSE circuit. In measuring a 240v home circuit there are two hot leads (L1 & L2). Do I need to measure both leads or can I just measure one leg?
  • SWEI
    SWEI Member Posts: 7,356
    If there's no neutral connection, you can measure the current on one leg.
  • andrewco
    andrewco Member Posts: 104
    Excellent. I'm thinking one of the below units as a good low cost way to monitor it's kWh usage.

    one
    two

    I was looking for a low cost alternative that would allow wireless monitoring or at least logging that can be automatically segmented by month or week but I haven't found it...at least not "low cost".
  • ratio
    ratio Member Posts: 3,777
    ISTR that a NC contact adjustable current switch was wanted for this project. I just came across an ACI part: A/ACSX and A/ASCSX. No clue as to pricing.

    For posterity, enjoy!

  • SWEI
    SWEI Member Posts: 7,356
    $97-$120 list on those depending on config. Great company, BTW.