How much make-up water is too much?

I would presume zero would be ideal. I have noticed that since my Burnham Megasteam was installed on 12/19, the hydrolevel vxt-120 auto water feeder meter has gone from 2 to 3. Is that a measurement in gallons? Too much?
Tagged:

Comments

  • SteamheadSteamhead Posts: 13,048Member
    These units usually read 002 fresh out of the box, so that's a net of one gallon. Not too bad, but it would be worth looking for a leaky vent or packing nut.
    All Steamed Up, Inc.
    "Reducing our country's energy consumption, one system at a time"
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Baltimore, MD (USA) and consulting anywhere.
    https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc
  • FredFred Posts: 7,874Member
    Is the water in the sight glass a little higher than it started out at, when the boiler is idle? New boilers need a lot of skimming to stabalize the water. It is possible that the boiler water is turbulant enough that it trips the water feeder during a heating cycle and then is slightly over-filled at the end of the heating cycle and all the condensate returns to the boiler.
  • Jamie HallJamie Hall Posts: 10,548Member
    That amount is not a problem. Granted, zero would be ideal, but... this is not an ideal world. And yes, that is in gallons.
    Jamie



    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.



    Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
  • BurntFingersBurntFingers Posts: 38Member
    Since the cold wave hit us, I've been loosing about 1/2 inch in my glass everyday. Checking chimney, it's good. I think it's spitting out my Gorton 2's.
  • SteamheadSteamhead Posts: 13,048Member
    Have you actually seen water or steam coming out of those vents?
    All Steamed Up, Inc.
    "Reducing our country's energy consumption, one system at a time"
    Steam, Vapor & Hot-Water Heating Specialists
    Oil & Gas Burner Service
    Baltimore, MD (USA) and consulting anywhere.
    https://heatinghelp.com/find-a-contractor/detail/all-steamed-up-inc