Woke up to a cold house this morning

Last night before I went to bed I thought I would modify the program the thermostat slightly by having a 2 degree setback from 10pm to 5:30am (going from 70 to 68). This morning we woke up cold with the house at 63 degrees. I went downstairs and saw on the thermostat that it was calling for Heat, went down to the boiler, took out my flat head screwdriver and slightly turned the cut-in screw on the pressuretrol half a turn and the boiler started up. I am stumped why this happened since the pressuretrol settings have been set the same for over a year. I did clean out the pigtail about a month ago as part of regular maintenance so I don't think that's an issue. The only "change" to the system was that I had a radiator added to the system on Monday - but the system worked fine Monday night through yesterday late evening. My wife even commented that she woke up in the middle of the night a few times to the air vent "whistling" so I think the boiler was working during the night until a point. I also noticed once I got the boiler firing this morning that the water in the sight glass almost disappeared. I assume this is due to the oil that may be in the boiler now from the pipework done earlier in the week (I know I will need to give it a good skim). Any ideas on why the boiler would not start firing until I adjusted the cut-in slightly? I know the Honeywell pressuretrols are not the most precise instruments but still feel it was strange that I needed to give it a slight adjustment. I have attached a pictures of the current "cut-in" setting plus pressure observed a few minutes after start-up plus sight glass.
0
Leave a Comment
Categories
- 80.9K THE MAIN WALL
- 2.5K A-C, Heat Pumps & Refrigeration
- 36 Biomass
- 394 Carbon Monoxide Awareness
- 2.6K Controls
- 1.4K Domestic Hot Water
- 3.7K Gas Heating
- 100 Geothermal
- 130 Indoor-Air Quality
- 2.3K Oil Heating
- 30 Pipe Deterioration
- 563 Plumbing
- 4.2K Radiant Heating
- 333 Solar
- 12.1K Strictly Steam
- 36 Water Quality
- 7 Industry Classes
- 51 Job Opportunities
- 7 Recall Announcements
Comments
The specific Pressuretrol you have is known for getting stuck like this if it's at the extreme low end of it's range.
Unfortunately they get a little flaky around 0.5 PSI or lower.
If you are running your system at this low of a pressure or lower and using the Pressurtrol to control it I would recommend getting a 0 to 4 PSI Vaporstat as they are more reliable at these pressures.
I've read that the Vaporstat's are the Cadillac's of the pressure control on a steam boiler - are they something a semi-handy person can install themselves? Is my understanding right that they work in conjunction with the pressurtrol?
If you want to use both, using the Pressuretrol as a backup you would buy the 1/4" brass fittings you need to connect both to your pigtail, or, use separate pigtails which is preferred.
As far as wiring, you would wire them in series so if either control trips the burner shuts down.
Customer creates a setback with thermostat. Boiler cut-out on pressure, and never cuts-in.
Ensure that cut-in setting is within the normal operating range of the control or replace the pressuretrol with a vaporstat.
http://forum.heatinghelp.com/discussion/128249/why-do-honeywell-vaporstats-suck-so-badly
Has reliability improved? If so, any model recommendations?
There are alternatives -- which are considerably more expensive.
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England.
Hoffman Equipped System (all original except boiler), Weil-Mclain 580, 2.75 gph Carlin, Vapourstat 0.5 -- 6.0 ounces per square inch
People complain when the "guvmint" makes companies get rid of mercury switches, but people also complain about the mercury in all fluorescent lights. I wonder how many CFLs you could make with a single mercury switch, a few thousand?
People are amazing.
A 5 PSI gauge is fine, but for 1.5 PSI I'd use a 0-3PSI gauge.
If it was my system and I had an oversized boiler that creates pressure while running I'd probably aim for 1.5 PSI off and 0.25 PSI on with a vaporstat. But you want the pressure to start climbing again before it bottoms out so it depends on how fast the system restarts and comes back to a boil.
It'll take some tweaking. I'd just want to keep it at 1.5 PSI or lower, while keeping the widest operating range possible.
As far as how low can the pressure go without sucking air back in on the off cycle, it depends on the system. Mine actually heats the house fine with only 0.006 PSI.
So your mission, should you choose to accept it, is to see how low you can get your vaporstat's cut-in without any of the radiators sucking air back in before the boiler gets back to producing steam.