Steam boiler replacement Princeton NJ
Dave0176
Member Posts: 1,178
They had this fairly young (1995) direct vented Burnham IN5. The boiler was sooo badly rotted that all but one section had two fist sized holes in it. I had told her that I was afraid to touch it in fear it may crumble lol. I wish I had pics of the old boiler but the mess of removing it and my hands forget it. EDR was 287 and she wanted a new installed radiator in her 1st floor bathroom right off the kitchen which had no heat either, so I put a Burnham slenderized 24 EDR rad in bringing total EDR to 311. So in went a Weil McLain EG40. We also replaced all the wet returns as I knew they'd be clogged, and when I cut them open I couldn't believe water actually returned back to the boiler.
DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......
3
Comments
-
-
Are you guys determined to replace every boiler in NJ? lol Always looks good Dave.2
-
@KC_Jones why not there are a ton of them here in nj that are poorly installed.2
-
Good on you both!0
-
if they are willing to pay for quality why stop?
Looks great.0 -
Ez I say that every time I walk down a dark dingy basement and I see the beast usually with the nice gold piping all around it, and even better I give the old installer credit as he respected the 80 year old piping by just ADAPTING to itEzzyT said:@KC_Jones why not there are a ton of them here in nj that are poorly installed.
But heck yeah KC were up to that challange.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
I hear yea Dave, about 50% of the steam and hydronic boilers I look at the systems themselves have hacked apart and the real challenge is to put everything back to the way there supposed to be0
-
beautiful work dave....paul sASM Mechanical Company
Located in Staten Island NY
Servicing all 5 boroughs of NYC.
347-692-4777
ASMMECHANICALCORP@GMAIL.COM
ASMHVACNYC.COM
https://heatinghelp.com/find-a-contractor/detail/asm-mechanical-company0 -
Another beauty!0
-
Very, very nice.New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com0 -
I'm the homeowner. Thank you, Dave--you did a fantastic job! Here's a picture of the old boiler.2
-
Nice to see your customer appreciates your work,as always looks great.What caused the failure in the original boiler.0
-
Going by the pictures I'd say #1 lack of proper water treatment and #2 perhaps too much makeup water.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
Maybe , but the cost cutting measure used in the iron did not help. Somewhere there is the sound of a high end Mercedes - Benz door slamming and a man with a smirk remembering the V series castings.ChrisJ said:Going by the pictures I'd say #1 lack of proper water treatment and #2 perhaps too much makeup water.
Beautiful change out b.t.w.
hvacfreak
Mechanical Enthusiast
Burnham MST 396 , 60 oz gauge , Tigerloop , Firomatic Check Valve , Mcdonnell Miller 67 lwco , Danfoss RA2k TRV'sEasyio FG20 Controller
1
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements