Only 2 months old

superdave
superdave Member Posts: 155
HI All,

This is from a indirect 80 Gal. tank that is only two months old. What are your thought???
jackrich99

Comments

  • Abracadabra
    Abracadabra Member Posts: 1,948
    What's water chemistry like? i assume this is for DHW?
  • Jamie Hall
    Jamie Hall Member Posts: 24,092
    check all your electrical grounds and bonding.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
    STEVEusaPACharlie from wmassGordy
  • Paul48
    Paul48 Member Posts: 4,469
    Yeah......I'd be checking the piping for voltage
  • lchmb
    lchmb Member Posts: 2,997
    were they getting a nasty smell? May need a magnesium rod..
    4Johnpipe
  • 4Johnpipe
    4Johnpipe Member Posts: 485
    Definitely get the water tested. The indirect manufacturer should have the recommended sacrificial rod for the results of the water test.
    LANGAN'S PLUMBING & HEATING LLC
    Considerate People, Considerate Service, Consider It Done!
    732-751-1560
    email: langansph@yahoo.com
    www.langansplumbing.com
  • Paul48
    Paul48 Member Posts: 4,469
    You might want to put an electric anode rod in there. More money but it's only once.
  • superdave
    superdave Member Posts: 155
    We are having the water tested. It is magnesium and we have electrical company come out and also do testing. The funny thing is no smell just getting a lot of air out of system that is what made us check rod.
    Charlie from wmassPaul48
  • kcopp
    kcopp Member Posts: 4,462
    What was in there before?
    How long did that last?
    What has changed?
  • superdave
    superdave Member Posts: 155
    I think it was 80 gal. before. Old tank was SS but the nipples was bad.

    The house had water damage for last years snow old boiler went off line and some of the radiators cracked. So we added a zone of radiant and changed out 12 radiators to new Baxi radiators and new Baxi 40-GA boiler with 79gal. Baxi tank.

    I know one wall was repaired by the gas and water meter then they installed spray foam insulation. I don't know if they removed the grounding wire.
  • superdave
    superdave Member Posts: 155
    Sorry the boiler is Baxi 1.33 GA. with tank.
  • ChrisJ
    ChrisJ Member Posts: 16,122
    Curious, how does a missing ground wire cause an anode rod to be attacked like this?
    Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment
  • 4Johnpipe
    4Johnpipe Member Posts: 485
    We have a water utility that treats with calcium carbonate we need aluminum anode rods or it turns hot water to seltzer water
    LANGAN'S PLUMBING & HEATING LLC
    Considerate People, Considerate Service, Consider It Done!
    732-751-1560
    email: langansph@yahoo.com
    www.langansplumbing.com
  • Harvey Ramer
    Harvey Ramer Member Posts: 2,261
    Sparkling water out of a faucet! How cool is that.
  • BobC
    BobC Member Posts: 5,491
    Probably taste pretty good with the branch water.

    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • Jamie Hall
    Jamie Hall Member Posts: 24,092
    ChrisJ said:

    Curious, how does a missing ground wire cause an anode rod to be attacked like this?



    It depends on how things are set up -- but if a bonding wire is missing on a water pipe, current may flow through the water itself -- and the anode rod is an excellent place for that to happen. This eats the anode rod away (and puts the anode metal -- often magnesium -- into the water, by the way). If everything is bonded, then the electricity would much rather flow through the wires, being even lazier than steam.
    Br. Jamie, osb
    Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England
  • superdave
    superdave Member Posts: 155
    So I am sending out the water to be tested for anything that might making this rod go. I do have a PH tester and will see what it reads.

    Also have an electrician coming out in the AM.

    Thanks All