Selection of a pump for a hot water loop off steam boiler
Abracadabra
Member Posts: 1,948
I've been requested to install a hot water loop off a steam boiler. Loop will be about 325-350' of 3/4 copper including the approx. 50' of slant/fin baseboard. What pump am I using here? I'll be pumping boiler condensate instead of going thru a heat exchanger, so I'll need a brass pump. What does everyone use? Standard B&G 100AB? Anything more efficient?
0
Comments
-
Stainless steel is a better price since brass now needs to be lead free. I have had good luck wit Taco 100 pumps in Stainless steel.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
Thanks @Charlie from wmass
You think a 110-24S would be sufficient for this application? hot water heat design is not my forte..
My concern is that this pump is rated for 33gpm @ 7ft head. I only need about 3gpm. How do I dial it down since pump is not variable speed
0 -
You don't dial it anywhere. You could use a heat exchanger to make it a closed system for the loop. Then you can use variable speed on the hot water side and the taco on the condensate side.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
Will the boiler accept a tankless coil? Then you do not need a three piece circulator.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0 -
Nope.. no coil available.. that would have been optimal. So when you are pumping condensate directly thru the loop, we're pushing ~30gpm? Doesn't that affect the BTU output of the fintube? I was thinking of using a couple of strategically placed globe valves to slow down the flow..Charlie from wmass said:Will the boiler accept a tankless coil? Then you do not need a three piece circulator.
0 -
I think.the pipe holds it back to around 12 gpm. It will be fine.Cost is what you spend , value is what you get.
cell # 413-841-6726
https://heatinghelp.com/find-a-contractor/detail/charles-garrity-plumbing-and-heating0
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 420 Carbon Monoxide Awareness
- 80 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 891 Plumbing
- 5.9K Radiant Heating
- 378 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements