Oil or Propane
I would go with LP. If you are able to per buy, you can usually avoid the price spikes. Plus LP to me, seams a lot cleaner to work on and service.
What type of system do you have. If you have an old radiator system, you could go with a modulating boiler and get into the 90% eff.
Whatever you decide, do your homework and don't let your tech lead you by the nose. Even new oil boilers can have add ins like outdoor reset, that will help with eff.0 -
Well.
I would get a second opinion on the boiler for sure. I have been doing this for 14 years and have yet to know how to predict when a cast iron boiler is going to start leaking. Maybe I need a crystall ball?
As for fuel choice there are alot of things to consider. Right now in my area (northern Ct) oil is cheaper than LP. If you consider LP make sure you budget purchasing the tank outright. Don't get me started on some of the things LP companies get away with around here as far as pricing, especially if you lease the tank.0 -
Oil at $2.32 per gallon, or l.p at$4.50 per gallon up here. Not even close to being a question which way to go. But if the l.p is cheap where you are at, then it would definitely be something to look at. If, you really did need a new boiler....
Rick0 -
I paid $.99/gallon for LP this past summer. I'm a gasser
myself. The way to make it most cost effective is to own your tank and bury it in your yard. That way you control the buy and aren't getting mid-season, every few week, fills at market price. That is a killer. As well, it is nice not having an oil tank in the house. 1 -
If you go with LP and NG becomes available some day, it would be an easy conversion.
With LP you can cook and dry laundry also.
I'm in N Wisconsin and Iron Mt MI driving past LP companies offering 99.9 per gallon. With a mild winter so far up here I'll bet that continues to go down.Bob "hot rod" Rohr
Living the hydronic dream0 -
That is a burnahm v8 series boiler if they cleaned the boiler and noticed a Crack it is possible to tell that it will leak soon these boilers (more so the v7 series )have cracks that don't always leak they open when the circulator run. Burnahm had a big problem with the v7 and v8 series in the late 90's and early 2000s . You can get a new burnahm at a discount from burnahm. The mpo is a much better boiler with efficiency around 86%. I would stay with oil the cost to remove tank bury propane tank and pipe house adds up when you can improve the efficiency with an new oil boiler for less upfront money. The price of propane can fluctuate just as much as oil. Oh BTW if you do replace the boiler make sure they do a load calculation an over sized boiler will cost more to operate.1
If fuel costs are similar then how's your chimney?
If you have a good interior chimney and nice clean basement then I might stay with oil.
If you're talking low temperature system then lp gets my vote.
Although i don't like how lp regulators freeze up once in a blue moon
It's all good0 -
Everyone I've ever seen with oil didn't have a nice clean basement. They usually have an oily stinky mess and a pile of kitty litter on the floor.GW said:If fuel costs are similar then how's your chimney?
It's all good
And then when it's time to service the boiler once or twice a year, that's a stinky dirty mess.Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
1 -
Switched to LP myself, from oil 2 years ago. We had a 50 year old oil boiler, it was time, and we didn't appreciate $800-$900 fill up invoices. Now we have more space in the garage, the new boiler is silent, hangs on the wall out of the way, no chimney worries. $1.69 per gallon. What's not to like?0
C'mon by, good buddy. I'll grant you it's not a McMansion recreation and theatre lounge, but it is a good clean usable basement -- for over 200 years old.ChrisJ said:
Thanks to everyone for all the great advice. As much as I want to get rid of that oil tank in my basement and as much as I want to lower my carbon footprint...I can't make the numbers work. I did some research on current fuel prices and boiler efficiency ratings and propane just doesn't measure up cost wise...at least not right now here in the Northeast. I know the site has a rule against discussing pricing...but I'm guessing that relates to labor and materials on installs, service etc. and not for general fuel price information? If so here's the math I did to figure out the cost of a million btu's. I took the fuels price per gallon and compared it to that fuels btu content and then to a typical efficiency rating on a boiler that uses that fuel. I found a Weil-Mclain oil boiler with an efficiency of 86.2 and a Weil-Mclain propane boiler with a rating 91, I did also find a Slant Fin High Efficiency wall hung propane boiler with a rating of 95.4 although that Slant Fin was 2x the cost of the other boilers. BTU assumptions were 138,690 per gallon of oil and 91,333 per gallon of propane. The price of fuel oil today is $2.18/gal. and the price of propane is $3.43/gal.
So I used the following math:
$ per gal. / (btu content * eff.rating)*1mm=Cost per 1mm btu's
Oil boiler
$2.18 / (138,690 * 86.2%)*1mm= $18.23 per million btu's
Propane boiler
$3.43 / (91,333 * 91%)*1mm=$41.27 per million btu's
High Eff wall hung Propane boiler
$3.43 / (91,333 * 95.4%)*1mm=$39.53 per million btu's
So if I'm looking at this correctly...heating with Propane at this point in time is roughly 2x the cost of heating with fuel oil. I know oil is at a very low price at the present time and I also realize that Propane is more expensive in the Northeast US than it is just about every where else. But using the same math as above I believe that Propane would have to be about 70% the price of oil to make it worth while. For example if oil were $3.00/gallon then Propane would be cheaper to heat with only if it were priced lower than $2.10/gallon ($3.00 * 70% = $2.10)
I'm I figuring this correctly? Am I missing anything?
Oil stains on the floor, wet spots on the lines or filter housing?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
AFUE may be a 'typical efficiency rating' but it does not make a very good predictor of actual fuel use. Net thermal efficiency differences between a modulating/condensing boiler and an on/off conventional boiler are 20% minimum, and usually more like 30%.Tgardiner65 said:I took the fuels price per gallon and compared it to that fuels btu content and then to a typical efficiency rating on a boiler that uses that fuel.
$15.72 per million BTUs versus $37.55 per million BTUs. No contest. Today. In your neighborhood.0 -
One small oil stain right at the filter. Dating from before when @Charlie from wmass and I were working on the system!ChrisJ said:
Oil stains on the floor, wet spots on the lines or filter housing?Br. Jamie, osb
Why not both, you could easily pipe in another boiler, fired by propane, high efficiency to be vented through the sidewall, and switch back and forth as prices fluctuate. I did this in my own house. But with oil prices low, I would wait until oil prices drastically increase, or when the boiler actually starts to leak, that could be many, many years.
Thanks, Bob GagnonTo learn more about this professional, click here to visit their ad in Find A Contractor.1 -
Chris in my parents house the furnace is in my fathers workshop (oil burner). I would eat off the floor anywhere in there including under the oil tank. House was built in '77 and there has never been a drop of oil on that concrete ever.ChrisJ said:
Oil stains on the floor, wet spots on the lines or filter housing?0 -
I don't know how propane is priced where you are but up here the price is based on usage the more you use the less you pay per gallon. Heating and hot water you should be cheaper than someone that is just cooking or drying clothes. I pay 1.79 for propane. It also helps if you own your own tank too.
2 -
Some Home Despot stores have 420# cylinders at a very good price. Used refurb 499s can be a steal.0
What are the downsides to owning your own tank?
How long are the tanks certified for before something needs to be replaced or inspected?
Will all LPG companies or states allow you to own a tank?
What is up with PA's 80% full rule?Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
DOT tanks come certified for 12 years, at which point they need a requal that is good for another 5, 7, or 12 years depending on the type of testing/inspection done.0
Sad that poor installs and service continue to give oil heat a bad rap. I would stay with oil unless natural comes into your picture in the future. He may be right with the up and coming leaker, but have him point it out0