Vaporstat Question
LPGasman
Member Posts: 18
I have a Peerless SC/SVT steam boiler It came factory equipped with a Honeywell PA404A pressuretrol ,indicator on front is set at 1/2 lb. no matter where the differential is set burner won't shut off till Gauge hit 3psi minimum. Boiler is 6 months old, pigtail is clear water level 1/2 way in gauge glass. the PA404 is mounted on a pigtail on top of the MM67
LWCO, some say it should be mounted higher above the water level. Some say install a vaporstat in place of the Pa404. System is 2 pipe . Looking for input
LWCO, some say it should be mounted higher above the water level. Some say install a vaporstat in place of the Pa404. System is 2 pipe . Looking for input
0
Comments
-
Do you have a good low pressure gauge on the boiler or are you seeing 3 PSI on the 0-30 PSI gauge?1
-
Pressuretrols have zero quality control at the bottom of the scale so they can be wildly inaccurate. Is the inside dial set to 1 or less?
If your going to try and calbrate it I suggest you add a 0-3PSI gauge beside the pressuretrol so you can see what is going on. One of our members came up with a method to calibrate pressuretrols -
http://forum.heatinghelp.com/discussion/149944/i-figured-out-how-to-calibrate-a-pressuretrol
Mounting a pressuretrol higher is good practice but it does nothing for it's accuracy.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
A pressuretrol can be calibrated to turn off at 1.5 and back on a 0.5, but it may take some fussing. Try that first.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I tried the differential dial in various position with little change. So any opinion as to which vaporstat I would need?0
-
What type of gauge are you verifying the pressure with? the 0-30 that came on the boiler or something with a much lower scale like 0-3 or 0-5? This does matter.0
-
Follow the recalibration procedure. It is simple and will take care of the issue. As has been said by KC, you need to have a 0-3 PSI gauge on the boiler for accuracy and for future monitoring of what your system is actually doing and as Jamie said, calibration is a little fussy but not that bad. Just make very minor adjustments using the hex screw.0
-
I am with Fred and KC_Jones. Vaporstats aren't cheap and your pressuretrol might be all right. What you need first is an accurate low-pressure gauge. Install, then get back to us.New England SteamWorks
Service, Installation, & Restoration of Steam Heating Systems
newenglandsteamworks.com0 -
When I was using a pressuretrol I was able to get it to operate at a low setting, but of course, not by using the scale. I turned the differential as low it would go. Then I turned the adjustment as low as it would go, right to the point to where the linkage started to get sloppy like it was going to fall apart. I ran the boiler long enough for it to shut off on pressure. Then, it would not restart. I adjusted the pressure just until the boiler restarted, then about a quarter turn more. This seemed to give a good operating point, shutting off at 1.5 psi and back on about .5 psi.Dave in Quad Cities, America
Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
http://grandviewdavenport.com0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements