Water Level in Gauge Glass
Attached is a picture of the gauge glass on my boiler (one pipe steam heat).
Is the water level too high. If so, how do I lower it?
Thanks!
Comments
-
That's fine. Anywhere from 1/4 from the top to 1/4 from the bottom when the boiler is off is just fine.
If you ever did have to drain some, there's sure to be a drain on there somewhere, but without seeing the whole setup I couldn't say where.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
If that's a Burnham the proper water level is 3/4 of the way up the glass.
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
The water appears to have a green tint. Are you using chemicals?--NBC0
-
I see no green tint there NBC?nicholas bonham-carter said:The water appears to have a green tint. Are you using chemicals?--NBC
Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
It must be my phone display.--NBC0
-
Thank you all. It is a Burnham IN6.
NBC - the water is clear now (I had actually just had it skimmed - it was installed in July and still had some oil showing up in the gauge glass).0 -
3/4 of the way up is where you want to be when the boiler is off. Make sure it's been off for 10-20 minutes before checking it.Jeff_H said:Thank you all. It is a Burnham IN6.
NBC - the water is clear now (I had actually just had it skimmed - it was installed in July and still had some oil showing up in the gauge glass).
I usually add to my system when it's a 1/2" low or so but I'm super anal.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
If you have the owner's manual, check it for the placement of that "Lowest permissable Water level" tag also. Where it is placed now is wrong. It should be on the panel, somewhere around mid way up the glass. Not an issue if you know where the water level should be, but a big issue for anyone who isn't familiar with that boiler.0
-
That low water tag looks to be a factory install with screws or rivets. "The lowest point is somewhere below the glass that you really can't see" now how does that work??0
-
I think it is drilled and installed by the installer. I have a Burnham and the tag is placed at just above the middle of the glass. If I were to let the water get as low as the tag in this picture, i'm pretty sure there'd be a UFO seen in the neighborhood on a cold winter day. That tag has to go somewhere above the LWCO probe.0
-
-
-
I know, with the LWCO operating, what is the sense to even have that sticker there. The actual water level has the sticker and also a dimple in the jacket.
FWIIW, I don't think the factory would want the installer to determine the water level in their boiler. And if I were the installer I would not want the responsibility of doing so. It seems that the physical dimensions of the block and amount of heat applied would set the water line.0 -
I'm not sure. I know my Burnham has several demples in the panel where one could drill for the various plates. I assummed some of those panels were interchangable with different boiler models and depending on which model you had, you drill for the plate accordingly. In no case would there be a sticker at or below the bottom of the sight glass. If there is a need for a plate anywhere on the sight glass, it should read " Normal Water Level" and be done with it.JUGHNE said:I know, with the LWCO operating, what is the sense to even have that sticker there. The actual water level has the sticker and also a dimple in the jacket.
FWIIW, I don't think the factory would want the installer to determine the water level in their boiler. And if I were the installer I would not want the responsibility of doing so. It seems that the physical dimensions of the block and amount of heat applied would set the water line.0 -
Putting the tag that says "Lowest Permissable Water level" below the bottom of the sight glass is not right and I know you know that. Some things are just not worth auguing about. Who else on this site would consider a water level below the sight glass, where you can't even see the water level, permissable for normal operation. I can not imagine any boiler manufacturer being willing to accept liability for tagging a "Permissible Water Level" at a point below the bottom of the sight glass where it isn't easily visable to the homeowner.0
-
Why not consult the manual, and find the proper waterline height/dimension from the boiler base, and check the label height?--NBC0
-
Couple of thoughts here... first, @nicholas bonham-carter has the right idea: find the manual and check it.
Second... the water level should be within the gauge glass. That's what the gauge glass is for. Exactly where in the gauge glass is considerably less important; there are very few applications where the water level is so critical that one has to really be fanatical about it.
Third, at least one of the low water cutoffs on the boiler should trip while the water is within the glass...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
I did for my boiler, a Burnham, and it shows it at just above half way up the sight glass and about 2" below the Normal water level and an inch or so above the MM67 LWCO, but my boiler is 33 years old. I also went out and looked at the I & O Manual for the new Burnham IN boilers and it shows them at about an inch, maybe 3/4" above the bottom of the sight glass. i didn't find any that suggest anywhere below the sight glass.nicholas bonham-carter said:Why not consult the manual, and find the proper waterline height/dimension from the boiler base, and check the label height?--NBC
0 -
Thank you all for your help.
Something I noticed is that from the time that I raised the question (about three weeks ago), the water level in the gauge glass (I have been checking it when the boiler is not running) has gone done. When I first posted, it was about two-thirds up the glass. Now it is just over half way up the glass. The good news is I don't see any water leaking from the boiler. Should this be of concern?
Thanks again.0 -
Probably not. Might be minor losses through vents, that sort of thing. The actual water usage by a boiler is somewhat variable -- a gallon a month seems pretty normal; a gallon a week is perhaps a little high but... meh... a gallon a day? That's a problem.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0
Categories
- All Categories
- 86K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 420 Carbon Monoxide Awareness
- 80 Chimneys & Flues
- 1.9K Domestic Hot Water
- 5.3K Gas Heating
- 96 Geothermal
- 154 Indoor-Air Quality
- 3.3K Oil Heating
- 60 Pipe Deterioration
- 891 Plumbing
- 5.9K Radiant Heating
- 378 Solar
- 14.7K Strictly Steam
- 3.2K Thermostats and Controls
- 52 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements