Radiator Capacity
ishmael1980
Member Posts: 13
Good morning,
Can anyone tell me the heating capacity of this radiator? It's a single pipe steam system and I'm considering using it to heat a 21FT x 13FT room. Thanks in advance.
Best,
Bob
Can anyone tell me the heating capacity of this radiator? It's a single pipe steam system and I'm considering using it to heat a 21FT x 13FT room. Thanks in advance.
Best,
Bob
0
Comments
-
What's the height?0
-
Good question Paul. I'll get the dimensions tonight. Thanks!0
-
You need to do a heat loss calculation for the room. Otherwise you won't know if it will heat the room properly.0
-
Thanks Paul. We're replacing the heating system and I know the plumber did the heat loss assessment for the entire house to size the boiler.0
-
That's good to know, but @Paul48 meant that you need a specific heat loss calculation for the individual room you want to use that radiator in.ishmael1980 said:Thanks Paul. We're replacing the heating system and I know the plumber did the heat loss assessment for the entire house to size the boiler.
0 -
I hope you mean the plumber added up the EDR of all the radiators in the house, and not the heat loss for the house. If this is steam, as you say it is, the ONLY way you can properly size the boiler is to the radiation.ishmael1980 said:Thanks Paul. We're replacing the heating system and I know the plumber did the heat loss assessment for the entire house to size the boiler.
Please please tell me that's what he did...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
That's cool looking radiator IMO!0
-
Well... he said "plumber" instead of "steam man" so.....Jamie Hall said:
I hope you mean the plumber added up the EDR of all the radiators in the house, and not the heat loss for the house. If this is steam, as you say it is, the ONLY way you can properly size the boiler is to the radiation.ishmael1980 said:Thanks Paul. We're replacing the heating system and I know the plumber did the heat loss assessment for the entire house to size the boiler.
Please please tell me that's what he did...
/me hides from all the plumbers on the board....
1 -
Thank you for the responses.
Jamie, the plumber doing the install was measuring and counting the sections of all the radiators but I thought that was for a heat loss calculation - I stand corrected on that. Thank you for enlightening me.
The radiator pictured above is 13" Tall x 12" Deep and 28" Wide. Can someone advise how I determine if the radiator is appropriately sized for my 21ft x 13ft kitchen?
Thanks again,
Bob
0 -
If my tables are right that radiator has an EDR of about 33 so it can put out about 8,000 BTU with steam. If your heat loss is that low it will work if the heat loss is higher you will be cold.
Do a heat loss on that room before committing to that radiator.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
Thank you Bob. Can you direct me to a reference on how to do a heat loss calculation?0
-
Some of us have had good success using the Slantfin app:
http://www.slantfin.com/index.php/professionals/heatlossPeerless 63-03, 118,000 BTU (308 sqft), single-pipe steam system connected to 286 EDR of radiation, 30ft of baseboard and indirect DHW
3PSI gauge0 -
Great. Thank you!0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements