Beckett Pump losing prime

cwazcwaz Posts: 11Member
Good morning all, I'm hoping to get a little holiday help here as this one's got me stumped. My Weil McLain has been running like a champ since September and all of a sudden I started having issues yesterday.
A quick synopsis: thermostat calls for heat, boiler kicks on, lock out button pops (as some point over night during the set back), I open the bleed valve for a few seconds, close it and she fires right up. After this process she will fire back up a as needed as the vaporstat takes control until the thermostat is satisfied. The priming issue only appears to occur during long periods of the boiler being shut off.
Any thoughts on why I'm losing prime?? I checked for leaks around the connections and valves but can't find any.
Luckily I've trained my wife how to prime the beast, might need to extend that training to my teenage girls lol. Thanks in advance! And Happy Thanksgiving to everyone.
Tagged:

Comments

  • Bob BonaBob Bona Posts: 2,081Member
    Describe the oil delivery piping.
  • cwazcwaz Posts: 11Member
    Bare, soft copper tubing from two stand alone Roth tanks, travels approximately 16" up from the top of the tanks to the bottom of the floor joists, travels parallel with the floor approximately 4 feet, takes a 90 degree turn, continues along the joists, drops 6' to the floor via another 90 degree bend, once at floor leve it takes another 90 degree bend on the surface of the cement floor ( a short portion runs through mortar "attaching" it to the side of the boiler slab), then takes another 90 degree bend up to the filter inlet.
    The portion running through the mortar is showing signs of corrosion, the copper is turning green, could it be there is a small leak there that is allowing air into the line during the long periods of inactivity?
  • Bob BonaBob Bona Posts: 2,081Member
    edited November 2015
    Any lift scenario demands an oil deareator. The issue only exacerbates as the tank level drops. You may or may not also have a minute air leak. Some checking with a vacuum gauge will reveal this.

    Providing the system is tight, your best insurance is a TigerLoop Ultra deareator.
  • HatterasguyHatterasguy Posts: 6,058Member
    I've suffered with this issue for nearly one year. The Tiger loop will permanently solve the problem but you will have never identified it.

    If you have a continuous run of copper tube from the oil level itself (inside the tank) to the filter, the problem lies between the filter and the pump inlet.

    My latest guess regarding this issue is the Firematic valve as I am 99% confident that there are no leaks in the filter or the piping from the filter to the pump.

    It only takes a tiny leak at that valve to accumulate sufficient air in a couple of weeks to cause the unit to go off on safety. Surprisingly, the pump does not appear to force any of this air through the nozzle.
  • Robert O'BrienRobert O'Brien Posts: 2,986Member
    Ridgid tubing in Roth?
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • EBEBRATT-EdEBEBRATT-Ed Posts: 3,896Member
    If your loosing your prime you have a leak plain and simple. Find it and fix it. Disconnect the piping and pressure test it. A tiger loop is just more unnecessary fittings, restrictions and places for a leak. The other fix is to make it a two pipe system as it will prime itself. (no one will agree with this)
  • HatterasguyHatterasguy Posts: 6,058Member

    The other fix is to make it a two pipe system as it will prime itself. (no one will agree with this)

    I agree. :)

    The only risk is the return piping. Anything that causes a break in that line pumps all the oil to China. It is a consideration today.
  • EBEBRATT-EdEBEBRATT-Ed Posts: 3,896Member
    true. but a leak in he suction line below the oil level will send the oil to north korea
  • HatterasguyHatterasguy Posts: 6,058Member

    true. but a leak in he suction line below the oil level will send the oil to north korea

    Well, that depends on your definition of a "leak". The OP has a leak in the suction line below the oil level............be sure of it............but there is no evidence of any oil discharge...........be sure of that as well.
  • BrewbeerBrewbeer Posts: 441Member
    Oil lines buried in concrete can corrode and leak if the oil line isn't sleeved or coated. Consider by-passing the section beneath the concrete.
    Hydronics inspired homeowner with self-designed high efficiency low temperature baseboard system and professionally installed mod-con boiler with indirect DHW. My system design thread: http://forum.heatinghelp.com/discussion/154385
    System Photo: https://us.v-cdn.net/5021738/uploads/FileUpload/79/451e1f19a1e5b345e0951fbe1ff6ca.jpg
  • Robert O'BrienRobert O'Brien Posts: 2,986Member
    edited November 2015
    Two ways this happens without an air leak.
    1. The oil is degassing under vacuum, as little as 4-5" can cause this
    2. Overhead oil lines are best avoided if possible, tiny air bubbles coalesce over a period of time into one large bubble in the horizontal portion of oil line. Even Tigerloops can be overwhelmed by this sudden appearance of a large quantity of air. Power bleeding can resolve this if it is due to the line not being purged of air.
    Steps to power bleed
    Bleed the system in the conventional manner
    - Close the valve at the tank
    - With the bleeder valve open, run the pump until a good vacuum develops
    - Open the tank valve
    - Repeat this process
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • Robert O'BrienRobert O'Brien Posts: 2,986Member

    "An oil burner that is supplied by an overhead oil line can develop unusual vacuum conditions over
    time. When setting up such a burner, the objective is to totally fill the overhead line so that there
    is a true siphon. However, if the overhead line is not totally purged, as the burner runs (and it
    could be months later) the vacuum can keep increasing until the pump is starved.
    As explained by Bruce Marshall of Suntec Pumps, with an overhead oil supply line on a single line
    system, it is not enough to just run a pump for a while until the bubbles stop coming out. The
    overhead portion may remain partially filled with air. In fact, the tubing may have filled with oil
    only as much as is needed to supply the pump and this means there could be a lot of air.
    The problem of excessive vacuum develops because, as the burner runs, microscopic air bubbles
    can escape from the oil, increasing the amount of air in the overhead portion of the supply line. It
    may take several months, but the available spaceî can be so small that vacuum readings can be
    excessive"
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • Bob BonaBob Bona Posts: 2,081Member
    Thank you Robert for putting it out there. In a lift situation, the pump runs the ragged edge on one pipe. Like Robert said, the oil becomes "stretched", foaming occurs, then pump cavitation, then game over.

    Tiger Loop devices should be SOP in any lift jobs. It is NOT a band aid or a means to cover over defective joints.
  • EBEBRATT-EdEBEBRATT-Ed Posts: 3,896Member
    What Bruce Marshall said is true however this will not happen if the oil line is sized correctly , happens with oversized lines. Hooked up one pipe an overhead line is only moving nozzle capacity .50, .75/hr is not much flow and I suppose you could collect bubbles. On two pipe your moving pump capacity say 7gph and you will have no such problem and will not need a tiger loop if the lines are 100% tight.

    Pumps and tanks stay cleaner with 2 pipe as you are constantly moving, pumping and filtering oil. Low flow lets sludge settle out.

    JMHO after 42 years and goes against conventional wisdom.
  • HatterasguyHatterasguy Posts: 6,058Member
    Bob Bona said:


    Tiger Loop devices should be SOP in any lift jobs. It is NOT a band aid or a means to cover over defective joints.

    A Tiger Loop is a bandaid to cover up defective joints in a simple lift of fuel by four feet from the bottom of the tank to the top of the tank. This is quite different than the overhead lift that Robert referenced above. i have several that operate perfectly OK in that condition for many years.

    All systems with a four foot maximum lift will run perfectly fine if there are no air leaks and no microscopic bubbles will form as the required vacuum of 3.62" Hg is quite low.
  • OilmonOilmon Posts: 2Member
    If every joint is tight, AND all air has been purged from the fuel supply run, the likely point of entrance of small amounts of air would be the pump seal itself. I have solved many single pipe, topline oil feed loss-of-prime issues with a fuel unit changeout. Even though there is not any evidence of FUEL leakage from the seal, they can and do sometimes allow small amounts of air in around the shaft, which accumulates inside the pump body until cavitation and loss of pumping ability ensue.
    That being said, however, a Tigerloop is a permanent solution to the problem , albeit a bit more costly.
  • Robert O'BrienRobert O'Brien Posts: 2,986Member
    No reason for 2 pipe systems to exist. The vacuum may be below the level that causes gassing but with 20GPH through the filter, how long until it loads up enough to cause problems? In addition, air that does pass through the pump and it does, plays havoc with combustion. Clean enough boilers that use 2 pipe and those using single or a tigerloop and get back to me.
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • HatterasguyHatterasguy Posts: 6,058Member
    edited November 2015

    In addition, air that does pass through the pump and it does, plays havoc with combustion. Clean enough boilers that use 2 pipe and those using single or a tigerloop and get back to me.

    If air would go through the pump, even a minute amount of it, we would never have the stated problem on one pipe and a Tiger Loop would never be necessary.

    The cleanliness, or lack thereof, of your boiler has nothing to do with one pipe or two pipe.
  • HatterasguyHatterasguy Posts: 6,058Member

    but with 20GPH through the filter, how long until it loads up enough to cause problems? .

    In theory, you would conclude that it loads up 50X faster than the one pipe.

    But, practice shows a different result.

    You can only clean oil once. If you flow 20 GPH, you clean all the oil in less than one day. The flow rate is so high that no additional sludge accumulates during that one day. So, after that one day elapses, and the filter has done 99% of the work and it basically coasts until it sees another oil delivery.

    The one pipe has to work for the entire time, albeit at a slower rate, to achieve the same result.

    So, the conclusion that it "loads up" more than a one pipe is factually incorrect. It will load faster than a one pipe but never more than a one pipe.
  • Robert O'BrienRobert O'Brien Posts: 2,986Member

    In addition, air that does pass through the pump and it does, plays havoc with combustion. Clean enough boilers that use 2 pipe and those using single or a tigerloop and get back to me.

    If air would go through the pump, even a minute amount of it, we would never have the stated problem on one pipe and a Tiger Loop would never be necessary.

    The cleanliness, or lack thereof, of your boiler has nothing to do with one pipe or two pipe.
    You're incorrect!
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • Robert O'BrienRobert O'Brien Posts: 2,986Member

    but with 20GPH through the filter, how long until it loads up enough to cause problems? .

    In theory, you would conclude that it loads up 50X faster than the one pipe.

    But, practice shows a different result.

    You can only clean oil once. If you flow 20 GPH, you clean all the oil in less than one day. The flow rate is so high that no additional sludge accumulates during that one day. So, after that one day elapses, and the filter has done 99% of the work and it basically coasts until it sees another oil delivery.

    The one pipe has to work for the entire time, albeit at a slower rate, to achieve the same result.

    So, the conclusion that it "loads up" more than a one pipe is factually incorrect. It will load faster than a one pipe but never more than a one pipe.
    Faster is more isn't it, when discussing an annual service interval?
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • HatterasguyHatterasguy Posts: 6,058Member

    In addition, air that does pass through the pump and it does, plays havoc with combustion. Clean enough boilers that use 2 pipe and those using single or a tigerloop and get back to me.

    If air would go through the pump, even a minute amount of it, we would never have the stated problem on one pipe and a Tiger Loop would never be necessary.

    The cleanliness, or lack thereof, of your boiler has nothing to do with one pipe or two pipe.
    You're incorrect!
    Maybe you'd like to explain why?
  • Bob BonaBob Bona Posts: 2,081Member
    I can't imagine any joints (copper) inside of a tank. The leak paths are typically from the duplex on. The Loop wasn't designed to circumvent poor joint makeup. If that were the case, you'd have drain back every off cycle and foam in the Loop chamber every start cycle.

    HUGE difference in filter load up between 2 pipe vs one pipe.

    Thoeretically the boiler cleanliness should have no bearing on piping but it does real world as the system ages. 
  • HatterasguyHatterasguy Posts: 6,058Member
    edited November 2015

    but with 20GPH through the filter, how long until it loads up enough to cause problems? .

    In theory, you would conclude that it loads up 50X faster than the one pipe.

    But, practice shows a different result.

    You can only clean oil once. If you flow 20 GPH, you clean all the oil in less than one day. The flow rate is so high that no additional sludge accumulates during that one day. So, after that one day elapses, and the filter has done 99% of the work and it basically coasts until it sees another oil delivery.

    The one pipe has to work for the entire time, albeit at a slower rate, to achieve the same result.

    So, the conclusion that it "loads up" more than a one pipe is factually incorrect. It will load faster than a one pipe but never more than a one pipe.
    Faster is more isn't it, when discussing an annual service interval?
    No, faster is not more.

    Faster only means that the filter loads up early. Think of a exponential curve. All of the massive filtering happens in the first 24 hours and then the curve flattens out to nothing.

    Now consider a one pipe. The filter gets a constant stream of debris for the entire time it stays in place. Think of a flat line.

    At the end of the day, both accumulated the same amount of debris.

    Now, I will grant you the fact that if you change an old tank over to two pipe, you're going to get a massive ingestion of debris from near the bottom of the tank due to the very high flow rate. But, other than this one example, neither filter is going to load more prior to the service interval.

    I have several of both and the two pipe goes just as long as the one pipe. I will note that the two pipe system is old as dirt so there is no accumulated debris to overwhelm the filter.

    I do have a story about the two pipe when we changed the outdoor tank. Found another used tank for cheap and installed it. Filled it with about 50 gallons of old oil from the old tank. Filter plugged and shut the boiler down in about one hour. Not surprising. Changed the filter and strainer and it's been fine ever since.

    The two pipe also has the distinct advantage of PREVENTING some sludge accumulation at the bottom of the tank due to the high flow rate.

    You fellows are biased against the two pipe for all the wrong reasons.
  • Robert O'BrienRobert O'Brien Posts: 2,986Member
    You are thinking of sludge as being in a fixed state and finite quantity.There are many different types of sludge, many are biological and hence reproduce.
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • EBEBRATT-EdEBEBRATT-Ed Posts: 3,896Member
    Hattersguy said"The two pipe also has the distinct advantage of PREVENTING some sludge accumulation at the bottom of the tank due to the high flow rate.

    You fellows are biased against the two pipe for all the wrong reasons. "

    I couldn't agree more. The old rule of thumb to me still applies, if you have lift use two pipe. If you don't have lift use 1 or pipe
  • HatterasguyHatterasguy Posts: 6,058Member
    edited November 2015

    You are thinking of sludge as being in a fixed state and finite quantity.There are many different types of sludge, many are biological and hence reproduce.

    And..........???

    Would I prefer to send it to the filter as soon as it develops or would i prefer to let it sit and accumulate on the bottom of the tank and pray that it never reaches the pickup tube?

    You're just being dishonest to the HO and kicking the can down the road. Someday he'll have to replace (or power flush) his tank due to your use of a one pipe system. It's inevitable.............just a matter of time.
  • Robert O'BrienRobert O'Brien Posts: 2,986Member

    You are thinking of sludge as being in a fixed state and finite quantity.There are many different types of sludge, many are biological and hence reproduce.

    And..........???

    Would I prefer to send it to the filter as soon as it develops or would i prefer to let it sit and accumulate on the bottom of the tank and pray that it never reaches the pickup tube?

    You're just being dishonest to the HO and kicking the can down the road. Someday he'll have to replace (or power flush) his tank due to your use of a one pipe system. It's inevitable.............just a matter of time.
    Fix 30 or 40 thousand oil burners and get back to me, you know nothing of what you speak.
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • HatterasguyHatterasguy Posts: 6,058Member

    You are thinking of sludge as being in a fixed state and finite quantity.There are many different types of sludge, many are biological and hence reproduce.

    And..........???

    Would I prefer to send it to the filter as soon as it develops or would i prefer to let it sit and accumulate on the bottom of the tank and pray that it never reaches the pickup tube?

    You're just being dishonest to the HO and kicking the can down the road. Someday he'll have to replace (or power flush) his tank due to your use of a one pipe system. It's inevitable.............just a matter of time.
    Fix 30 or 40 thousand oil burners and get back to me, you know nothing of what you speak.
    Doing the wrong thing 30 or 40 thousand times doesn't make you any better at it.

    You still don't have a technical reason for using one pipe. I use both and I know the advantages and disadvantages of both. Keeping the tank clean is most definitely not the purvey of a one tank system.
  • Robert O'BrienRobert O'Brien Posts: 2,986Member

    You are thinking of sludge as being in a fixed state and finite quantity.There are many different types of sludge, many are biological and hence reproduce.

    And..........???

    Would I prefer to send it to the filter as soon as it develops or would i prefer to let it sit and accumulate on the bottom of the tank and pray that it never reaches the pickup tube?

    You're just being dishonest to the HO and kicking the can down the road. Someday he'll have to replace (or power flush) his tank due to your use of a one pipe system. It's inevitable.............just a matter of time.
    Fix 30 or 40 thousand oil burners and get back to me, you know nothing of what you speak.
    Doing the wrong thing 30 or 40 thousand times doesn't make you any better at it.

    You still don't have a technical reason for using one pipe. I use both and I know the advantages and disadvantages of both. Keeping the tank clean is most definitely not the purvey of a one tank system.
    Just as you repeating the same misinformation ad nauseum doesn't make it right!
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • HatterasguyHatterasguy Posts: 6,058Member

    You are thinking of sludge as being in a fixed state and finite quantity.There are many different types of sludge, many are biological and hence reproduce.

    And..........???

    Would I prefer to send it to the filter as soon as it develops or would i prefer to let it sit and accumulate on the bottom of the tank and pray that it never reaches the pickup tube?

    You're just being dishonest to the HO and kicking the can down the road. Someday he'll have to replace (or power flush) his tank due to your use of a one pipe system. It's inevitable.............just a matter of time.
    Fix 30 or 40 thousand oil burners and get back to me, you know nothing of what you speak.
    Doing the wrong thing 30 or 40 thousand times doesn't make you any better at it.

    You still don't have a technical reason for using one pipe. I use both and I know the advantages and disadvantages of both. Keeping the tank clean is most definitely not the purvey of a one tank system.
    Just as you repeating the same misinformation ad nauseum doesn't make it right!
    There was no "misinformation" given and you have failed to refute any of it.

  • spoon22spoon22 Posts: 32Member
    I agree with Robert 100 percent 2 pipe is not the way to go it does clog filters faster in fact you need a bigger filter with 2 pipe because you have tripled the gph trough it. Add to that the added expense time and risk of leak not to mention oil siphon backwards at time of tune up there is no need for 2 pipe especially when there are other options for lift like a tigerloop. BTW you will never clean the tank with the filter proper additives and treatments will the filter is supposed to protect nozzle and fuel pump not clean the tank
  • HatterasguyHatterasguy Posts: 6,058Member
    edited November 2015
    spoon22 said:

    I agree with Robert 100 percent 2 pipe is not the way to go it does clog filters faster in fact you need a bigger filter with 2 pipe because you have tripled the gph trough it.

    Actually, you flow about 50X through it............

    I ask you a simple question.

    Once you filtered all the oil from a delivery on a two pipe system, where does the additional material come from to "clog the filter faster"?

    Once the oil is clean, the filter doesn't accumulate any additional debris from the oil (unless the tank has a massive sludge issue).

    I use the same filters on one pipe as I do on two pipe. Both easily last the year. The one pipe tank continually accumulates sludge in the bottom and I am now at the point of blowing the sludge away from the pickup tube. It's only a matter of time.................

    The one pipe kicks the can down the road. Someday, the HO will pay for that privilege.


    BTW, I also avoid the two pipe system when I can for the reasons that you noted above. It's a bit of a tradeoff in terms of risk versus reward. The two pipe definitely causes you pause if you consider the risk of a "problem" on the return line.

    There really isn't a single solution for every installation but the two pipe most definitely keeps the oil in the tank cleaner over the long haul.
  • Robert O'BrienRobert O'Brien Posts: 2,986Member
    Some sales pitch in there but the info about air in pumps and nozzle lines is spot on.

    http://www.westwoodproducts.com/images/tigerloop_is_reliability_us.pdf
    To learn more about this professional, click here to visit their ad in Find A Contractor.
  • Bob BonaBob Bona Posts: 2,081Member
    Perfect, Robert.
  • HatterasguyHatterasguy Posts: 6,058Member
    edited November 2015
    Interesting display.

    Here is where I have a question about it:

    The company suggests that "when oil is drawn up from the oil tank large amounts of gas bubbles can be released from the oil".

    OK.

    Where does this large amount of air go?

    They further show a display of the pump chamber that is 1/2 full of oil and suggest that any air will rise to the top of the pump chamber and expose the inlet to the gearset.

    OK.

    So, I ask the simple question:

    How does any burner function at all based upon their description? Large amount of gas bubbles are being released but any air that accumulates in the pump chamber will eventually open the port to the gearset.


    They further show air bubbles in the nozzle line in diagram one. By their own explanations, this can only happen when the oil in the pump chamber drops below the level of the port to the gearset. At that point the burner is close to shutdown anyway. It most certainly cannot be considered normal operation.


    Don't believe everything you read.