    That's good to hear, glad you figured out the wiring conundrum.

    I wish there was a way to set a minimum on time for the VisionPro 8000, but I suppose messing with the CPH setting will allow you to approximate.
    Peerless 63-03, 118,000 BTU (308 sqft), single-pipe steam system connected to 286 EDR of radiation, 30ft of baseboard and indirect DHW
    3PSI gauge
  • LarryK
    LarryK Member Posts: 46
    I think they amount to the same thing. But the minimum on-time approach seems more direct. If it takes 15 min for your system to really get going then you set it for that. Or a little more or less. You're not stuck with integer divisions of an hour.