need to pull control wire from manifold to boiler area before closing in will cat 6 work or what do

Options
keyote
keyote Member Posts: 659
closing in a manifold top floor access will not be as easy later what type of wire do i need to pull for controls might be 4 wire actuators zone valves ? worst case scenario

Comments

  • hvacfreak2
    hvacfreak2 Member Posts: 500
    Options
    Decent 18 gauge stranded copper or low capacitance alloy ( Trane Purple ). Shield is not necessary if these are binary ( on / off ) but if they are proportional ( analog ) it might be worth the little extra.
    hvacfreak

    Mechanical Enthusiast

    Burnham MST 396 , 60 oz gauge , Tigerloop , Firomatic Check Valve , Mcdonnell Miller 67 lwco , Danfoss RA2k TRV's

    Easyio FG20 Controller

  • keyote
    keyote Member Posts: 659
    Options
    how many wire and do i need to pull say one four wire for each actuator
  • Zman
    Zman Member Posts: 7,569
    Options
    You would be safe running 4 conductors per valve.
    Assuming all the end switches will be tied together, the bare minimum would be 2 per valve and 2 for all the end switches.