  • Put a Gorton #2 on an antler with the present vent, and see if that does the trick. Ideally you need 2 Gorton #2's with the length of the piping.--NBC
    j a_2
  • Fred
    Fred Member Posts: 8,542
    Adding additional vents won't hurt, as long as they are needed but I suspect you are not going to improve system operation much until that near boiler piping is fixed. The way it is now, the very short header is probably not above the normal water line, of the boiler, at the recommended heigth, that reducer on that header holds a lot of water, right under the riser to the main. The steam has to be very wet, taking all that water up into the main.
  • Dave0176
    Dave0176 Member Posts: 1,178
    You should definitely vent the mains much more, however radiator venting may be a trial and error type of thing. I vent the rads based on cfm of air in the pipe and radiator, I also take into consideration the location. Sometimes it comes down to the homeowner just playing with different vents over time to get it right.
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

    I cannot force people to spend money, I can only suggest how to spend it wisely.......
  • Main vent location.