Adding Mixing control (Tekmar 356) to regulate water temperature to radiant

Options
sma1123
sma1123 Member Posts: 4
I'm a homeowner with a new radiant subfloor install. System is noisy with pex expansion. Plumbing company rep mentioned using a mixing control (Tekmar 356) with outdoor reset to regulate the temperature of the water to help with potential expansion noises. (Boiler is navien mod/con) Is this something that can be added post-design or does it require a complete repiping?

Comments

  • Rich_49
    Rich_49 Member Posts: 2,766
    Options
    Is the whole house radiant floor ? What model Navien do you have ? Why does your radiant floor not have outdoor reset installed originally ? What circulator/s are currently being used ?

    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC
    732-751-1560
    Serving most of New Jersey, Eastern Pa .
    Consultation, Design & Installation anywhere
    Rich McGrath 732-581-3833
    IronmanSWEI
  • Ironman
    Ironman Member Posts: 7,376
    Options
    I have to ask the same question as Rich: why wasn't ODR installed with the floor? Or with the Navien?

    If there are no other zones but the floor, the mod/con can control ODR with the optional outdoor sensor installed and setup properly.

    If you have to use the Tekmar 356, then repiping and an additional circ is required.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • sma1123
    sma1123 Member Posts: 4
    Options
    There is an outdoor reset. It was probably a stupid question. I assumed that the tekmar complemented the ODR. I am not that knowledgeable. The noises happen when the heating cycles. when it's steady no issues ... it's awesome. Incredible warmth. Stays on 2-3 hours and then i hear the thermostat click and the noises start for 10 minutes so. It's very annoying especially taking a nap on the couch. It's only one floor of radiant with baseboard upstairs. The rep said this term 'injection control' to regulate the temperature so it sounded like something different. I do have ODR and mixing control so that sounds like it does the same thing.