Need wiring diagram for L8148J1009 Aquarelay to add Field vent damper
The Steam Whisperer
Member Posts: 1,215
Just trying to make a few upgrades before winter and tried this last night and didn't get the wiring right.
To learn more about this professional, click here to visit their ad in Find A Contractor.
0
Comments
-
thanks for the link to the diagrams....I had to put together 3 diagrams to get the wiring sorted out, but I have it working now.To learn more about this professional, click here to visit their ad in Find A Contractor.0
-
You can't use an L8148J Universal replacement relay with a vent damper. The reason is the primary control (L8148J) does not have an internal fuse which must blow on the first call for heat. All controls that contain a place for a damper have such a fuse. The blowing of the fuse prevents operation of the equipment if the damper is not attached to the equipment.0