Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.
Need wiring diagram for L8148J1009 Aquarelay to add Field vent damper
The Steam Whisperer
Member Posts: 1,249
Just trying to make a few upgrades before winter and tried this last night and didn't get the wiring right.
To learn more about this professional, click here to visit their ad in Find A Contractor.
0
Comments
-
thanks for the link to the diagrams....I had to put together 3 diagrams to get the wiring sorted out, but I have it working now.To learn more about this professional, click here to visit their ad in Find A Contractor.0
-
You can't use an L8148J Universal replacement relay with a vent damper. The reason is the primary control (L8148J) does not have an internal fuse which must blow on the first call for heat. All controls that contain a place for a damper have such a fuse. The blowing of the fuse prevents operation of the equipment if the damper is not attached to the equipment.0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements