maxitrol 325 Q....
kcopp
Member Posts: 4,472
in Gas Heating
In order for a Maxitrol 325 L # to " regulator to work....must you have 2# of gas feeding it? Can you have standard gas pressure on one side to start then have it boosted later?
I have a job where the existing gas line in a home crawlspace is undersized. I need to add a couple appliances. Tankless WH and a gas range....
The house is occupied and want to add these but at the same time the gas company will not just run out there and make the regulator changes when I ask.
Can I install them then get the gas company to run by in a couple days?
ty,kcopp
I have a job where the existing gas line in a home crawlspace is undersized. I need to add a couple appliances. Tankless WH and a gas range....
The house is occupied and want to add these but at the same time the gas company will not just run out there and make the regulator changes when I ask.
Can I install them then get the gas company to run by in a couple days?
ty,kcopp
0
Comments
-
Volume is where you will be lacking with the undersized line. Pressure from the meter should be OK, as long as the correct size gas line is installed to accommodate the total of the new appliances.0
-
Great. That's what I needed to know. They will certainty have to pick and choose what they want to run and when....at least until the gas company gets out there. Hopefully that is a matter of a couple days.... not weeks.0
-
Kcopp, is it a hard to work place, This crawlspace?0
-
yes. 30" all crushed stone. +50' from one end to the other. Meter on one end the new gas range (108k) and tankless (60k) gas dryer (30k) and a fha furnace on the other. Plus another fha in the middle. 1 1/4" gas main the length. Needs to be 1 1/2"0
-
What happens if you use.5 pressure loss instead of .3 per Nat.Fuel? Would that 1 1/4 work or is it border line? Jus curious.0
-
You might try Size-It to double check the gas line size. It's made to size csst, but it has a hybrid style, a piped main with csst runs to the equip. I guessed at a few things, and it comes up with 1-1/4 at .5" drop. That won't help with low inlet pressure to the regulator, but it might keep you out of the crawlspace!0
-
That would be great but the water heater is 160K (my typo) ....you have 60K.
BTW. That is a great program....0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements