Another replacement with an added hot water loop

Options
Dave0176
edited October 2015 in Strictly Steam
Thanks all for recommending me to Dan, he is a cool dude and I was very happy to help him out.

Old boiler was a Utica PEG 112, 112,000 input, rather large for his home, EDR came in at 193. I installed a Weil McLain EG30.
I couldn't make heads or tails of the way the old boiler was piped, two mains were counter flow, one was parallel flow. And all came off the basically vertical header. The one counter flow I repiped to run off the main and re pitched it to drip into a wet return, the other counter flow had to stay that way, only I piped it properly. Finally we added a new hot water loop to give the basement some heat. Only bad thing about the whole job was the dang brand new pump relay was bad outta the box. Forgot to mention we added a 2 stage gas valve also.
DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

I cannot force people to spend money, I can only suggest how to spend it wisely.......
ChrisJ

Comments

  • Dave that is some beautiful work. I've run into the same situation with the relays right out of the box being bad.
    E-Travis Mechanical LLC
    Etravismechanical@gmail.com
    201-887-8856
    Dave0176
  • Beautiful Dave.How do you sell this system,King Valves etc.I know the price of materials etc is real high and the competition on the low end would not do half of what you did.Does it take a lot of educating the customers or is it a job where budget is not an issue.Whats the magic trick cause when you are allowed to do the right job great things happen and its not even work its a pleasure to do it.Thanks for sharing.
    Dave0176
  • It looks beautiful. I'm sure the homeowner is happy!
  • Looks great. Why such a big pump tho?
  • Bronze pump I did it once and inspector told me I was out of my mind.Maybe but isn't it supposed to be bronze.
  • I was always told hot water loop off steam boiler you need the B&G 100 AB 3 piece pump due to acidic boiler water which will kill water bearing pumps and cast iron pumps.
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

    I cannot force people to spend money, I can only suggest how to spend it wisely.......
    jonny88
  • That's a pretty one!
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
    Dave0176
  • Rarely do you see it though Dave.
  • jonny88 said:

    Rarely do you see it though Dave.

    I hear ya Jonny I follow Dans instructions to a tee for the hot water loop, never have had problem.
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

    I cannot force people to spend money, I can only suggest how to spend it wisely.......
  • Dave0176 said:

    I was always told hot water loop off steam boiler you need the B&G 100 AB 3 piece pump due to acidic boiler water which will kill water bearing pumps and cast iron pumps.

    Very nice install Dave, but now you got me worried about the stainless steel pump on my loop. Have you ever experienced failure with pumps in this setup in the past? I have two, one for my indirect DHW and my baseboard zone, both Taco 005 pumps.
    Peerless 63-03, 118,000 BTU (308 sqft), single-pipe steam system connected to 286 EDR of radiation, 30ft of baseboard and indirect DHW
    3PSI gauge
  • Circ is good, but I'd be a tad concerned about those iron fittings next to it...
  • SWEI said:

    Circ is good, but I'd be a tad concerned about those iron fittings next to it...

    What would you have done differently?

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • SWEI said:

    Circ is good, but I'd be a tad concerned about those iron fittings next to it...

    Idk the Flo Controls are cast iron too?
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

    I cannot force people to spend money, I can only suggest how to spend it wisely.......
  • Dave0176 said:

    SWEI said:

    Circ is good, but I'd be a tad concerned about those iron fittings next to it...

    Idk the Flo Controls are cast iron too?
    .............as are all the wet returns.

    Unless we pipe it all in copper and bronze................

    http://www.supplyhouse.com/Bell-Gossett-107037-1-NPT-Bronze-HydroTrol-Flow-Control-Valve-8620000-p
    Hmm what about the block that's cast iron lol....
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

    I cannot force people to spend money, I can only suggest how to spend it wisely.......
  • Dave0176 said:

    Dave0176 said:

    SWEI said:

    Circ is good, but I'd be a tad concerned about those iron fittings next to it...

    Idk the Flo Controls are cast iron too?
    .............as are all the wet returns.

    Unless we pipe it all in copper and bronze................

    http://www.supplyhouse.com/Bell-Gossett-107037-1-NPT-Bronze-HydroTrol-Flow-Control-Valve-8620000-p
    Hmm what about the block that's cast iron lol....
    Damn...........can't do much about that.

    How about we convince ECR to produce a bronze boiler?

    Now, you'd have a 50 year product.

    Be worth it not to deal with the rust BS.
    True Lmao,, I just wouldn't want to pay for it....
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

    I cannot force people to spend money, I can only suggest how to spend it wisely.......
  • Bio
    Bio
    edited October 2015
    Damn...........can't do much about that.

    How about we convince ECR to produce a bronze boiler?

    Now, you'd have a 50 year product.

    Be worth it not to deal with the rust BS.

    Hey, I remember seeing an old water heater made out of copper , leads me to believe that someone was going to that direction


  • The original subway cars in Boston were made of brass, they were replaced in the 70's. Can you imagine what that would cost now?

    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
  • Oooo, bronze steamer.

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • And Chris drifts off into his dreamland....
    2014 Weil Mclain EG-40
    EcoSteam ES-20 Advanced Boiler Control
    Boiler pictures updated 2/21/15
    ChrisJ
  • honesty, I don't like it...why did someone pipe the first 90s off the risers at such crazy angles...Perhaps this was piped with nipples...and no threading machine...on site...jmo
  • j a said:

    honesty, I don't like it...why did someone pipe the first 90s off the risers at such crazy angles...Perhaps this was piped with nipples...and no threading machine...on site...jmo

    Please explain yourself a bit better before you criticize a job I killed myself on.!!!!
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

    I cannot force people to spend money, I can only suggest how to spend it wisely.......
  • I did explain myself,re read the post...hay that's just my opinion,so I stated it
  • I have a 300 machine that comes on all jobs and gets used. As far the crazy angles? This system was a counter flow that was repiped many years ago leaving some of the counter flow and the rest re piped as a parallel flow. The HO had just completely finished the basement in dry wall, so no way we were re piping the rest of the system.

    As we speak the HO has told me this system is dead quiet, heats in mins and is great improvement over what had existed. I did my job and accomplished my goals.
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

    I cannot force people to spend money, I can only suggest how to spend it wisely.......
  • I'd be very happy to have a boiler piped like that in my cellar.

    Bob
    Smith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
    Vaporstat with a 12oz cut-out and 4oz cut-in
    3PSI gauge
    Dave0176RobG
  • I am sure it works perfect, and only commented on the angle of the riser fittings, can't see where the angle would effect the heat...that's all I was saying...nothing else
  • What crazy angles?

    Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.

  • Take it easy guys, I just posted my opinion on the picture that was posted...that's all....just because I dint like it doesn't make it wrong...Dave stated why the crazy angle, I am sure it's working fine
  • Fred said:

    It looks beautiful. I'm sure the homeowner is happy!

    You are correct. The homeowner (me) is very happy. Dave, thanks again for your excellent work. And thanks to everyone on this site that recommended Dave. It has been a real pleasure working with someone that has so much passion and knowledge of steam systems.
    vr608RobG
  • vr608 said:

    Have you ever experienced failure with pumps in this setup in the past? I have two, one for my indirect DHW and my baseboard zone, both Taco 005 pumps.

    Never got an answer to this. Anyone know whether stainless steel pumps used in this application are any good long term?
    Peerless 63-03, 118,000 BTU (308 sqft), single-pipe steam system connected to 286 EDR of radiation, 30ft of baseboard and indirect DHW
    3PSI gauge
  • vr608 said:

    vr608 said:

    Have you ever experienced failure with pumps in this setup in the past? I have two, one for my indirect DHW and my baseboard zone, both Taco 005 pumps.

    Never got an answer to this. Anyone know whether stainless steel pumps used in this application are any good long term?
    From what I understand the small cartridge pump bearings are water lubricated, so in a steam system the acidic boiler water eats the bearings. For what your using them for there probably fine.
    DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
    NJ Master HVACR Lic# 4630
    Specializing in Steam Heating, Serving the residents of New Jersey
    https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc

    https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter

    I cannot force people to spend money, I can only suggest how to spend it wisely.......
  • Cool, thanks for the info. I'll have to keep an eye on them as well as test the acidity of my system periodically.
    Peerless 63-03, 118,000 BTU (308 sqft), single-pipe steam system connected to 286 EDR of radiation, 30ft of baseboard and indirect DHW
    3PSI gauge
  • Beautiful job @Dave0176 . Love the vaporstat setup.