  • Dave in QCA
    Dave in QCA Member Posts: 1,786
    Options
    As in the words of the great Suzanna Roseannadanna..... Never mind.

    Actually, I missed the close bull headed TEE and thought others were referring to the one way down the line. On the one way down the line.....Since the split is 3 and 2.5, it is not as bad as an equal bull head. Not the best way for it to be piped, but leave it alone.

    Definitely fix the one near the boiler. Sorry for adding confusion to the mix!
    Dave in Quad Cities, America
    Weil-McLain 680 with Riello 2-stage burner, December 2012. Firing rate=375MBH Low, 690MBH Hi.
    System = Early Dunham 2-pipe Vacuo-Vapor (inlet and outlet both at bottom of radiators) Traps are Dunham #2 rebuilt w. Barnes-Jones Cage Units, Dunham-Bush 1E, Mepco 1E, and Armstrong TS-2. All valves haveTunstall orifices sized at 8 oz.
    Current connected load EDR= 1,259 sq ft, Original system EDR = 2,100 sq ft Vaporstat, 13 oz cutout, 4 oz cutin - Temp. control Tekmar 279.
    http://grandviewdavenport.com
  • cubicacres
    cubicacres Member Posts: 358
    Options
    No problem-the clarification is always appreciated.

    To fix the one near the boiler you mentioned-would that mean running a second main line all the way from the far BULL TEE about 20 feet down the main back to the boiler BULL TEE so the first main section has 2 pipes? Or is there just another pipe configuration that would be better to head down to the equalizer that's not the current setup, requiring only a few feet of pipe changes?
  • Fred
    Fred Member Posts: 8,542
    Options

    No problem-the clarification is always appreciated.

    To fix the one near the boiler you mentioned-would that mean running a second main line all the way from the far BULL TEE about 20 feet down the main back to the boiler BULL TEE so the first main section has 2 pipes? Or is there just another pipe configuration that would be better to head down to the equalizer that's not the current setup, requiring only a few feet of pipe changes?

    If you are talking to one of the skilled Steam Pros about doing this installation, let him decide how best to resovle any piping issues like those Bull Tees. Changing the piping to the equalizer isn't going to correct steam flow once its out in the system and it hits a Bull Tee.