Red expansion tank?

overpop
overpop Member Posts: 52
So I get the Purepro kit that has all the inlet/spirovent goodies only to read "don't install this expansion tank with radiant use the red one" I did install to get it up and running, Should I get the red tank?

Comments

  • Ironman
    Ironman Member Posts: 7,547
    Only if you wanna pay 3 times as much for it. "Radiant" tanks are recommend when there's more severe conditions such as: glycol, solar, etc.
    As long as your tank is sized sufficiently, and you don't have those conditions, you'll be OK.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • SWEI
    SWEI Member Posts: 7,356
    ...or if you have a system with non-barrier tubing.
    Ironman
  • Ironman
    Ironman Member Posts: 7,547
    That's definitely one of those more severe conditions. In that scenario, I'd use one rated for potable and 180* water.
    Bob Boan
    You can choose to do what you want, but you cannot choose the consequences.
  • overpop
    overpop Member Posts: 52
    Thanks guys answers that question! a few more to follow...sorry....