Pressurization test
overpop
Member Posts: 52
I have installed a boiler and I want to air test it before filling it with water. Does the Spirovent prevent pressurization or do I have to bypass this?
Thanks in advance...
Thanks in advance...
0
Comments
-
-
Yup, now I get why there are threads on top! Was wondering that. The pressure relief valve on the boiler says 30 psi, how much air psi can you give it to test?0
-
Why not just go 5 PSI or so over what your operating pressure will be?
Single pipe 392sqft system with an EG-40 rated for 325sqft and it's silent and balanced at all times.
0 -
ChrisJ oddly thats exactly what my instinct said to do, so I put 20 psi in (at the moment bypassing the spirovent), it's holding and I will check it in the morning. Thanks for the advice! My first complete boiler install (plumbing & electrical) and it came out nice. Learned a bunch (Pumping Away), but what helped is that I used to install movie theater projection systems. High voltage, low voltage, heavy cast Iron and, in some installs there was a circulator pump that would pump water through the film gate to keep it cool. 35 mmFilm, running at 24 frames a second about 2 feet of film per second, would be warm as it exited the projector. The gate and trap had to be cooled or the film would buckle and focus problems would occur.0
-
I spent many years in a projector booth. Never had the luxury of water cooled apertures, maybe on a combo 70/35 projector that I might have been near occasionally. This was all carbon-arc light source and it would only melt film if it broke and was stuck in the gate. Now try that with old nitrate film and you might as well throw gas on it to put it out. Safety film was a great invention. The old projectionists claimed that nitrate has better color rendition than safety film, but they had older eyes/tastes. Color perception has changed in 50 years. The color of light bulbs is a good example, we have went from yellow to blue/white in preference.
Just did the electrical/hvac in our new 67 seat one screen theater with digital & 3-D, surround sound with more speakers than we needed or paid for. Talk about a leap forward from our old 35 mm. Although we did have the late 1950's 3-D which was short lived, thank God.
(Yes, we are a small town). My grandkids can not envision a theater with only one screen.1
Categories
- All Categories
- 86.5K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 423 Carbon Monoxide Awareness
- 96 Chimneys & Flues
- 2K Domestic Hot Water
- 5.5K Gas Heating
- 101 Geothermal
- 157 Indoor-Air Quality
- 3.5K Oil Heating
- 64 Pipe Deterioration
- 928 Plumbing
- 6.1K Radiant Heating
- 384 Solar
- 15.2K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 42 Industry Classes
- 48 Job Opportunities
- 17 Recall Announcements