Repipe Thoughts?
tgbrew
Member Posts: 43
I’m posting this as a new thread because I think it got lost when I did it as a comment on the old string. Apologies for being annoying. I would love to get an opinion before I start buying fittings and want to get this going before autumn sets in.
This is a 2.5" header and I didn't include the unions, but there will definitely be a few scattered about. Does anything stand out to anyone who has done this? Design look OK?
This is a 2.5" header and I didn't include the unions, but there will definitely be a few scattered about. Does anything stand out to anyone who has done this? Design look OK?
0
Comments
-
I would change as noted on sketch and this is how we do it.Gennady Tsakh
Absolute Mechanical Co. Inc.2 -
lost one arrow. you must have at least 3 pipe diameters before and after take off tee. install isolation valves on return and supply. make provisions for boiler blow downs and return line blow down.
after connection of second steam supply to header increase header size as mentioned in Hatterasguy post.Gennady Tsakh
Absolute Mechanical Co. Inc.0 -
Spend just a tiny bit more and increase the equalizer piping from 1-1/4 to 1-1/2".
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
Thanks for the details! Indeed I drew it badly and plan for the equalizer to be 2" with 1.25" for the Hartford loop to match the return.
I tried to have the drawings match the design recommendation diagram from the manual. Their details didn't have those 3" spacings around the second riser and recommended a 2.5" header for this size boiler (187k btu). I just want to make sure it is OK to increase the header size.
Many thanks!!0 -
Ok- here are the changes. I think this is it, so definitely scream if something looks weird. I might not do the odd 90-degree turn for the second riser to get to the header and just try to fit a diagonal.
Thanks and I appreciate the help!
0 -
-
Minimum for what? I'm exceeding the Utica requirements for riser height, header size and spacings. What am I missing? I don't want to have to redo this...
Thanks!0 -
Nice. Many thanks!! I think I'm going to go with an 18" diagonal on the second riser, which would move the connection to the header closer to the first riser as you suggest. Thanks to everyone again. I'll post a pic I get these old pipes out and the new ones up.0
-
-
Very nice piping job, I'm sure you will much happier this winter.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
It looks good , have you fired it yet ? I noticed that a few posts above someone said to not use a reducing 90 at the end .
I was wondering how critical that area is , the last 90 down to the equalizer ? Can a tee be used here ( using the branch as the 90 and plug at the end ) for the purpose of cleaning or chemical fill ?hvacfreak
Mechanical Enthusiast
Burnham MST 396 , 60 oz gauge , Tigerloop , Firomatic Check Valve , Mcdonnell Miller 67 lwco , Danfoss RA2k TRV'sEasyio FG20 Controller
0 -
I used a 3" to 2" reducing 90 here and don't know why it would be a problem as long as it's pointed straight down.hvacfreak2 said:It looks good , have you fired it yet ? I noticed that a few posts above someone said to not use a reducing 90 at the end .
I was wondering how critical that area is , the last 90 down to the equalizer ? Can a tee be used here ( using the branch as the 90 and plug at the end ) for the purpose of cleaning or chemical fill ?
A tee should work fine as well. The objective is to drain the header into the equalizer as fast and completely as possible.Single pipe quasi-vapor system. Typical operating pressure 0.14 - 0.43 oz. EcoSteam ES-20 Advanced Control for Residential Steam boilers. Rectorseal Steamaster water treatment0 -
As far as I know a reducing elbow pointed straight down is not a problem, it's when people lay them on their side that it becomes problematic in that it can hold water.0
-
I haven't re-read the post but do you only have one main?0
-
It looks Great!0
-
Here is how I prefer to do it, just my preference.DL Mechanical LLC Heating, Cooling and Plumbing 732-266-5386
NJ Master HVACR Lic# 4630
Specializing in Steam Heating, Serving the residents of New Jersey
https://heatinghelp.com/find-a-contractor/detail/dl-mechanical-llc
https://m.facebook.com/DL-Mechanical-LLC-315309995326627/?ref=content_filter
I cannot force people to spend money, I can only suggest how to spend it wisely.......0 -
Very nice piping job neat and clean work0
-
Thanks everyone. Yes, we have fired and all seems well. No issues but not sure if it is helping our balance issue. The previous piping was pretty ridiculous.
We have one main and don't think the reducing tee is an issue. Not sure how else I would have done since I wanted the big header.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements