Navien combi will not heat house above 68, ran constantly from November to April
hudsoncorp
Member Posts: 15
Navien combi NCB 210, Serial # 7965201408041060, Engraved plate inside unit: 56321Built 2014Serial #
15055201407252067
Would not heat the house above 68 degrees all last winter, 62 in cold snaps
Contractor has walked away
Cold weather coming, need to know what's wrong & get it replaced with a cast iron boiler
Point Pleasant NJ
Exit 98 off Garden State Parkway
15055201407252067
Would not heat the house above 68 degrees all last winter, 62 in cold snaps
Contractor has walked away
Cold weather coming, need to know what's wrong & get it replaced with a cast iron boiler
Point Pleasant NJ
Exit 98 off Garden State Parkway
0
Comments
-
-
Thanks for the comments!
1940's, 1400 sq ft., brick, well insulated crawl, some insulation in attic
How do I reach Snowmelt?0 -
-
Contractor claims it is state of the art!0
-
-
What do you see that is wrong? System is one continuous zone. Suggestions?0
-
I'm assuming baseboard?
How many floors?0 -
Condensate neutralizer is not doing a lot of good in a vertical position. Needs to be horizontal with inlet bottom and outlet top. Or vertical with a trap on the outlet to force the neutralizer to stay mostly full.
What kind of emitters do you have? Those Navien combis only produce nameplate BTUS on a low temp emitter system. They are limited to about 5 gpm through the boiler.3 -
1 floor, old cast iron covered with steel baseboards, some Slantfin sections added0
-
Harry: How to find out what emitters they used?0
-
-
do you know what the supply water temp is?0
-
Probably the water filter--blue pex--originally they had it filtering the baseboard water! Now bypassed.0
-
Tommy: Yes-single story home0
-
No....the black pipe that comes out of the navien, then tees off.0
-
Get yourself some strap on thermometers or a laser thermometer gun. Turn you thermostat up as high as it will go. Let the boiler run for 20-30 minutes. Then measure the boiler supply and return on the boiler loop. Also measure the supply and return on the system piping.
Report back.0 -
Paul: If you're talking about the black pipe almost dead center, tees off to the left to a ball valve, it's the gas line0
-
. Min firing rate on that boiler is 18,000 btus I'm thinking it's short cycling like crazy, but that's me assuming
Also boiler will tell you on the display screen the supply water temp.0 -
Harvey: I'll try to get temps tomorrow0
-
No.....Behind the ball valve for the gas. The pipe tees to the left and goes up.0
-
Hudson ,
Contact me ! I'll be in Point Wednesday and would like to take a closer look .You didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38332 -
-
Paul: Low water cut off to top left of unit0
-
-
-
Thank you all for your comments! I will check again later for any updates.0
-
Care to elaborate Hat? I fail to see the system react as you described.Hatterasguy said:The problem with the system is the fact that it is most likely overpumped and the DT is smaller than 20. This results in the boiler modulating itself down.
A proper DT circulator will fix your issue.0 -
That sounds plausible at first, but if the boiler doubled its firing rate because you widened the delta T, then wouldn't the the delta T be the same as before and the boiler would then reduce its firing rate again?Hatterasguy said:
Sure.Harvey Ramer said:
Care to elaborate Hat? I fail to see the system react as you described.Hatterasguy said:The problem with the system is the fact that it is most likely overpumped and the DT is smaller than 20. This results in the boiler modulating itself down.
A proper DT circulator will fix your issue.
If that big B&G results in a system DT of 10, the Navien will immediately modulate downward to compensate. Remember, it has a constant flow rate of 5 gpm on the onboard pump, so, with a DT of 10, it only needs to put out 25K to meet the specified SWT. But, 25K won't heat the house.
Slow the pump down, get a DT of 20, and the output of the Navien doubles to 50K.
The dangers of being overpumped on a mod-con...........rearing its ugly head again.
Most of them won't put out anywhere near their specifications without a huge system DT (which may not be obtainable).
We had a similar discussion on the Viessmann last winter with a fellow who was cold all the time. It had to have a system DT of 35 if you wanted its full output. He didn't have it.
This NCB-210 offers a DOE of 95K. But, the only way you ever get it is with a DT of 38. Good luck with that.
Bob Boan
You can choose to do what you want, but you cannot choose the consequences.0 -
Been down this road before........Widening the DT with the pump, leaves more btus at the boiler. And now the buffer tank guys usually chime in. It's deja vu all over again!0
-
Mr. Hudson,
Did you take the temp measurements?0 -
-
Well...........What was the verdict? I think I speak for everyone, when I say I'm dying to know.0
-
Yeah, fill us in.0
-
Pretty much Paul.0
-
I too am waiting for their conclusions. Given the existing conditions, a mod con should never have been considered. High temp water & cast iron boiler appears to be the answer. Now I have to get it replaced or a refund of $10,200.00. I expect Rich or John will post when they are ready.
Thanks to all!0 -
Rich will fill you guys in more on this. Several obvious issues... System is a mono-flow with globe style "T's". Major air issue as the scoop cannot remove in current position and lacking a good manual purge set up. Had sporadic temps and the boiler return was reading higher than supply. Did read 20* DT at start up. Not happy with a single size secondary loop seems to be sending too much return back to boiler. Hydrolic separator would have been preferred or at least up-size the secondary loop. With a max temp of 194 and the existing construction would have recommended low temp baseboard. I would guess the original boiler was set to 210* or so...LANGAN'S PLUMBING & HEATING LLC
Considerate People, Considerate Service, Consider It Done!
732-751-1560
email: langansph@yahoo.com
www.langansplumbing.com1 -
I would certainly upgrade to a higher efficiency air purger. Even installed properly, those scoop type do not remove micro bubbles. A boiler like that and a mono-flo system really cry out for 90% plus air removal.
What model is that circ? It may not be oversized?Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
The only reason your present boiler is not heating your home is that it is not supplying the emitters with water at the required temp(usually about 180). Your old boiler was putting out those type of temps and your radiation was designed for those temps.You have to find a way to increase the supply temp or add more radiation.Most mod con boilers are designed to put out about 130 degree water and that will not do it.1
-
Could it be a simple as the wrong reset curve selected or programmed? Or the high temperature operation capability was not activated with the correct venting used?0
-
There are several reasons why this boiler is not heating this house . Not just one . This boiler is not utilizing outdoor reset so that is not an issue . Boiler was not connected to odr last winter either . This is a much more complex multitude of problems that touches every part of this system and most importantly whom the guys are proclaiming to know what they are doing that don't . These contractors were given a green light to do the Cadillac job yet did not perform their due dilligence to recommend and install the right combination of stuff .
I will post everything that is pertinent by this evening .You didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38332
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 916 Plumbing
- 6K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements