Hydronic Panel Radiator placement in a large room
Scott_Mountain_View_CA
Member Posts: 202
I'm heating a 725 sq ft great room with Rutal panel rads. One one end of the room is a long exterior wall. I've read that it's best to position panel rads on exterior walls, but if i did this I would have no panels on the opposite of the 23' long room, an interior wall with heated rooms on the other side. How important is it to put rads on both ends of a large room, rather than placing them just on the exterior wall with windows?
Attached is a layout showing Rutal wall panels under 2 exterior wall windows. There is sufficient BTUH output from these 2 rads to meet great room total heat loss at design. The fireplace is a high quality gas log set which puts out substantial heat (not factored into the heating equation).
Do I need a panel at the opposite end of the room?
Attached is a layout showing Rutal wall panels under 2 exterior wall windows. There is sufficient BTUH output from these 2 rads to meet great room total heat loss at design. The fireplace is a high quality gas log set which puts out substantial heat (not factored into the heating equation).
Do I need a panel at the opposite end of the room?
0
Comments
-
I can't open the XLSX spread sheet, so am speaking somewhat blindly. In an ideal situation, you want to place the radiator on the coolest potential wall to raise the MRT, and avoid your body seeing the lower MRT associated with outside walls, windows etc.
With that said, I have successfully placed radiators on inside walls and not received any complaints from the end users. Try posting the picture in another format, and I will try and look at it again later today.
In the radiant floor world, we typically place the highest water temperatures near the outside walls first and work our way inward. I had an errant employee who did a whole house completely backwards, introducing the hottest water in the core and working its way toward the outlying walls. I decided to let it ride and see if the consumer complained. During my first year checkup, I asked the consumer how they liked their system, and their response was "Fantastic comfort"...
I think maybe placement is not as critical as most people would have us believe. My first radiant wall project had ALL the radiant walls on internal walls, and it too works like a champ.
In my own home, I have radiant walls on the inside walls,and although I can sense where the radiant energy is coming from (I am more cognizant about these things than most people) it is nice and comfortable. Of course, I have radiant windows that are on the outside walls, and I think that has a LOT to do with the increased MRT and associated comfort.
YMMV...
METhere was an error rendering this rich post.
0 -
Radiant energy travels in all directions at the speed of light.
A good analogy is steeping out of the shade into the sunlight on a cold winter day. You feel the radiant energy transfer almost immediately.
With most panel rads you get both the radiant energy transfer and some convection. The convection will move the heat energy throughout the room.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream0 -
Mark, PDF file attached.
I'm trying to avoid adding a third rad in the portion of the room at the bottom of the drawing due to logistic issues. If I had to install a 3rd rad it would be positioned where noted.
Design temp = 39 degrees. Heat loss = 13 BTUH/sq ft.
0 -
Bob, were you able to view my room layout? Do you believe the positioning of the 2 rads will provide a comfortable space through the room? Notice the sofa area is not in line of sight to the rads....does this mean that area will be heated by convection and not radiation? Does it matter from a comfort perspective?0
-
Just crank up the entertainment center for additional btu's
Two will work. That 3rd one facing the fireplace may not add enough comfort for the hassle. Cover the load with enough radiator output and the room will heat.Bob "hot rod" Rohr
trainer for Caleffi NA
Living the hydronic dream1 -
Thanks Bob. The 2 rads cover the heat load requirement. I'm runnin' with it.0
-
-
LOL....my 50" plasma tv heats the room on a cool fall evening. I guess I'm buying expensive Runtals for those 9 annual design days0
-
-
Sounds like it's time to get a 70" TV. Lol0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements