Welcome! Here are the website rules, as well as some tips for using this forum.
Need to contact us? Visit https://heatinghelp.com/contact-us/.
Click here to Find a Contractor in your area.

Navien ch-240. Too much pressure.

bwdh20
bwdh20 Member Posts: 11
I have a Navien ch-240 combination heater.

I am getting too much pressure into the machine. Blew the 30 psi relief valive and with a higher psi relief the machine reads 58 psi.
«1

Comments

  • Rich_49
    Rich_49 Member Posts: 2,769
    Got a picture of the unit and near boiler piping and accessories ? These would help .
    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC
    732-751-1560
    Serving most of New Jersey, Eastern Pa .
    Consultation, Design & Installation anywhere
    Rich McGrath 732-581-3833
  • 4Johnpipe
    4Johnpipe Member Posts: 485
    Is this a new install? 58 PSI is pretty standard city water pressure. Is there a pressure reducing valve?
    LANGAN'S PLUMBING & HEATING LLC
    Considerate People, Considerate Service, Consider It Done!
    732-751-1560
    email: langansph@yahoo.com
    www.langansplumbing.com
  • JStar
    JStar Member Posts: 2,752
    edited August 2015
    Please don't put a bigger relief valve on. That is incredibly dangerous. Put the 30psi valve back on immediately, or shut the system down and call a competent technician to work it.
    RobG
  • Xmytruck
    Xmytruck Member Posts: 85
    Make sure you report which pressure valve went off the direct hot water should be 150psi. The space heating should be 30 psi, if that's the one that went off you most likely have a bad expansion tank shake the tank to tell if it waterlogged. Must have been cold if you turned your heat on in Aug.


    my direct hot water pressure valve on my NCB 240 went off last week but the town has been messing with the water pressure. Had a plumber check it out he basically tested the valve and gave it the thumbs up.
  • njtommy
    njtommy Member Posts: 1,105
    edited August 2015
    Could be a couple of things.

    I believe the CH-240 has a make up water valve built in to the unit and controls its own pressure from there.

    If your water make up, is piped external of the unit in a more traditional boiler set up I would say bad expansion tank.

    I would also look into a cracked heat exchanger where your boiler water and domestic hot water are now mixing together.
  • bwdh20
    bwdh20 Member Posts: 11
    1)it is the "boiler" relief valve, and yes I realize I should not have a 120 psi on there.

    2)It is not a new install, over 3 years, so while I never really paid attention to the psi previously, I figure it was not at 58 psi before the relief valve blew. I had the thought of a bad pressure regulator, but I didn't see anything in the manual that said one was built in. Error message says check water pressure sensor, though I question if that is the culprit or just a symptom of the high pressure in the system.

    3)Definitely possible the heat went on, thanks to a thermostat left at 65 ish while the AC was cranked up so a bad expansion tank is a good lead.

    Really appreciate the responses.
  • bwdh20
    bwdh20 Member Posts: 11
    As an extension of the above, as per the safety issue, the machine shut's itself down with the high pressure. so the unit is not currently running.
  • gennady
    gennady Member Posts: 839
    1.Test heat exchanger for DHW
    2. Test automatic feeder
    3. Test expansion tank.
    4. Leave 30 psi safety valve in place.
  • bwdh20
    bwdh20 Member Posts: 11
    Welp, i replaced the expansion tank and water pressure sensor, and still the problem exists.

    By isolating the water lines I've come to realize the pressure shoots up when the DHW cold water inlet is opened. So could the problem be the flow sensor? Or is it(as has been mentioned) the dhw heat exchanger?.

    I'll be talking to Navien again tomorrow, so I figure I'll track it down then, but the exchanges here have helped me gain an understanding of the unit, so again, all responses are much appreciated.
  • njtommy
    njtommy Member Posts: 1,105
    Sounds like it's time for a new heat exchanger.
    Rich_49
  • bwdh20
    bwdh20 Member Posts: 11
    Difficult install?

  • Rich_49
    Rich_49 Member Posts: 2,769
    Maybe the diverting valve which switches the unit from Space heating to DHW is settled in a bad place . These valves have been suspect or downright malfunctioned before .
    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC
    732-751-1560
    Serving most of New Jersey, Eastern Pa .
    Consultation, Design & Installation anywhere
    Rich McGrath 732-581-3833
  • JStar
    JStar Member Posts: 2,752
    But the diverter valve is completely on the boiler side.
    Rich_49
  • Rich_49
    Rich_49 Member Posts: 2,769
    New Plate HX and follow the recommendation for =<40 psi on the domestic side .
    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC
    732-751-1560
    Serving most of New Jersey, Eastern Pa .
    Consultation, Design & Installation anywhere
    Rich McGrath 732-581-3833
  • bwdh20
    bwdh20 Member Posts: 11
    Ya cracked plate in the heat exchange was the diagnosis, part on it's way. install tomorrow.

    How do I limit psi for domestic side?
  • Rich_49
    Rich_49 Member Posts: 2,769
    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC
    732-751-1560
    Serving most of New Jersey, Eastern Pa .
    Consultation, Design & Installation anywhere
    Rich McGrath 732-581-3833
  • Xmytruck
    Xmytruck Member Posts: 85
    edited August 2015
    Which heat exchanger failed primary secondary or hot water? Why do you need a pressure reducing valve out of curiosity? I'm surprising The company did not replace the unit. Did the company state you have too much pressure on the domestic side ?
  • jonny88
    jonny88 Member Posts: 1,139
    Hate to be a hater but not a Navien fan.But they do have good support and I guess for a boiler that costs about $400 to make they can well afford to replace parts.Send a pic of install.
  • Rich_49
    Rich_49 Member Posts: 2,769
    They do have plenty of practice in the support and warranty departments . Not to mention the very experienced recall department since more than 100,000 units have been recalled since introduction in the US . 2013 ,13,000 units due to carbon monoxide issue .
    You didn't get what you didn't pay for and it will never be what you thought it would .
    Langans Plumbing & Heating LLC
    732-751-1560
    Serving most of New Jersey, Eastern Pa .
    Consultation, Design & Installation anywhere
    Rich McGrath 732-581-3833
    SWEI
  • jonny88
    jonny88 Member Posts: 1,139
    Wow Rich I didn't realize they were that bad hence the constant changes to their unit.What an incredible marketing team though and have definitly shaken up the market.Feel bad for the consumer though.
  • Xmytruck
    Xmytruck Member Posts: 85
    edited August 2015
    The funny thing is that plumbers still install them and recommend them. I am on my second unit and have no confidence. my hot water pressure value went off two weeks ago and my installer told me nothing is wrong and to keep eye on it. All I hear about the unit is that there great and millions are installed without issues. I personally have had nothing but issues (crack HX, manifold leaks, etc)with the brand I will never use them again. when I got the unit installed three local companies highly recommend navien only one recommend WM97. Wish I went the wm97.
  • Snowmelt
    Snowmelt Member Posts: 1,425
    Manifold? they dont come with there own manifold. they do have an aftermarket manifold but it made from watts
  • jonny88
    jonny88 Member Posts: 1,139
    edited August 2015
    Unfortunately to many people come here after the fact.Heres the scoop,supply houses (not all)are interested only in sales.Of course there should be no issues in the first couple of years but after that try and get your installer back.A lot of people call it s throw away it but that's the competition.I have 3 supply houses in a 5 mile radius and this is their number 1 seller..Easy install etc and unfortunatly the homeowner is at their mercy.On a daily basis guys in the field see some crazy stuff that is why some threads here get heated as the good guys are frustrated and competing against low lifes
  • njtommy
    njtommy Member Posts: 1,105
    I have a Navien Ncb combi in my house. It's been in now for a year and I really like it a lot. I guess only time will tell. It does seem like they have come a long way.
  • Xmytruck
    Xmytruck Member Posts: 85
    edited August 2015
    John the way your reply reads is that the majority of plumbers are lowlifes. If navian is the best seller in your area or why are people installing them. My only conclusion is that plumbers know the issues and they know they're going to cash in. The plumber who installed mine is a good guy and been my plumber for six years and he scratches his head every time he comes to my house.


    Tommy
    Have had mine installed since Feb and I have gotten two e515 error codes. The quick install manifold start leaking and my hot water pressure value leaked two weeks ago. My plumbers response to the error codes the new systems are computers and they need to be reset once in a while. His reponse to hot water pressure value was "most plumbers would just open the valve and hit with their pilers and if leaks again to call". I have zero confidence in the unit and in my installer.
  • jonny88
    jonny88 Member Posts: 1,139
    Ask Gennady what his thoughts are on the unit.You won't get better info
  • njtommy
    njtommy Member Posts: 1,105
    edited August 2015
    Knock on wood I've not had a single problem. I work as a Commercial hvacr service tech. I installed my unit after reading the the installation manual several times. I also have water treatment in my boiler and for domestic water I have a well that gets filtered and treated.
    I also did combustion test and confirmed has pressures. Every thing was in spec as per there directions.
  • bwdh20
    bwdh20 Member Posts: 11
    Install complete. Bit of a pain, but not terrible. Unfortuneately still no freaking how water, (it did fire up the boiler side) call Navien they say it's either x or y(I kind of forget, three way valve or some circuitry) and I need a multimeter to test one of the two( the circuitry thing).

    Got the multi meter and about to call back. Getting a bit peeved. If I need more parts I won't see hot water till Monday at best.

  • bwdh20
    bwdh20 Member Posts: 11
    New issue is the flow sensor. Works intermittently. I do wonder if it was jostled during installation of heat exchanger. And I am still hoping the issue clears up the more it is used.

    I must say the technical service has been very helpful and they send parts without much question.

    But the machine, which had not been a problem before, has been a major pain this past week.
  • j a_2
    j a_2 Member Posts: 1,801
    The mod cons are here to stay, who knows maybe even someday they will be required, as opposed to cast iron..Imay have missed the post but how was this unit sized, Can u find in the program how many times this unit has cycled..Sounds like to me unles you get this under control, you may be in for a long cold winter...If I were I would insist on a new unit..They may be willing to swap it out, provided it was installed to specs
    by a qualified installer, with permit..I hope it was
  • jonny88
    jonny88 Member Posts: 1,139
    Come on @ j a permits, qualified installer ,sizing ,you know better than that.Buy unit ask for advice from counter guy and away you go.(tongue in cheek and not aimed at poster of thread).You can always call a service rep they will come and help you out.Iron out the kinks now before winter comes you dont want to address than on a below freezing night.Take some pics of install plz and whats your location they usually have field guys out there who will do repair and Navienpicks up bill.
    Good luck with it.
    j a_2
  • j a_2
    j a_2 Member Posts: 1,801
    Correct, shame on me...lol...happy Friday...You to Rich...happy Friday.. And thank you..Seriously..
  • bwdh20
    bwdh20 Member Posts: 11
    The unit was installed by a licensed plumber. I assume it was sized right, I've never had problems with lack of heat or hotwater in 3.5 years of use. 2000 sq' of heating and 2 showers. No washing machine no dishwasher. So I kind of doubt the thing is undersized.

    Would overuse make the heat plate crack?
  • bwdh20
    bwdh20 Member Posts: 11
    As far as ironing out kinks. Yeah I'm glad this happened in august.

    Really really hoping the flow sensor is the last issue.

    Looking at the 30 yr old Wells McClain combo boiler/dhw sitting next to it(2 family house) with much more appreciation. Yeah it's bigger and it's prob not as efficient(though my heating bill is pretty darn low) but I've had no issues with that in 14ish years of use.
  • Snowmelt
    Snowmelt Member Posts: 1,425
    bwd, you said your unit was installed by a license plumber, plumbers are not technicians. one of the only things plumbers are qualified for is venting of waist pipe. in reality accept for the back flow, which now I can do with my hvac license a master plumber is not a license boiler installer
    njtommyRobGRich_494Johnpipej a_2delta T
  • jonny88
    jonny88 Member Posts: 1,139
    Snowmelt thankgod I am qualified to vent waste pipe now I have to find someone qualified to install it...
    RobG
  • RobG
    RobG Member Posts: 1,850
    jonny88 said:

    Snowmelt thankgod I am qualified to vent waste pipe now I have to find someone qualified to install it...

    @jonny88, at least you can spell "waist pipe" correctly and use proper grammar! :*
  • jonny88
    jonny88 Member Posts: 1,139
    Honestly Rob I couldn't give a crap about grammar or spelling.Some of the finest mechanics I have worked with have little schooling partly because trade school was done away with a long time ago.I do take offense when a HVAC guy is way of base with a statement like that.Of course a Lic Plumber has to school himself on hydronics etc and for the most part a lot of us do or else we have the sense to call in a designer and work in tandem like Rich etc.But remember you need a Lic to run gas pipe so if you don't have it the plumber who is covering your **** in my opinion should be reported unless he is doing the gas work himself.Its a topic that has been discussed extensively here so please refrain from stupid statements saying we are unqualified.There is truth to the statement but again there are many threads related to this topic so lets not bring it up again.Remember without a Lic you should not touch gas pipe.
  • j a_2
    j a_2 Member Posts: 1,801
    Me being just a dumb plumber is trying to figure out if someone here is posting nonsense about licenced plumbers...That's just plain wrong..But I have been known to post before thinking...Remember I am just a plumber