Dead shorts....
under the hood, this is what is inside the tip of those sensors. I suppose if someone put 120V to one it could short it out, and read as a dead short.
A nail thru the wire somewhere? Or a bad splice where two wires touch.
If the control reads 888.8 you have an open circuit
88.8 is a short in the wire.
If they are PT1000 sensors it will rad 1000 ohms at 32F. Put the tip in a glass of ice.
At 212F it will read 1385, put the tip in a couple of boiling water.
This way you check both ends of the temperature range.
Possibly from extreme over-heating on an vac tube array it could damage the sensor tip?Bob "hot rod" Rohr
Living the hydronic dream0 -
sensor exposedBob "hot rod" Rohr
Thanks Hot rod.
Theses are two different units.
1 is a Stecca control w/ an 8 Buderus flat plate array.
The other a Puritan Controller on a Evac tube array...
Nails are possible but not probable. They worked fine for a few years then just stopped.
I need to follow some wires around...0 -
check for any sensor wire splices outdoors. I've seen the wire melt against the copper tube near the collector. That would show a short. Or if they get wet inside a taped splice.
If you must splice outside use the automotive "weatherproof" trailer wiring splices. Or the small button type, telcom splice that the phone company uses.Bob "hot rod" Rohr
You're going to have to unhook the sensor to check it and the wiring for faults separately.
The manual should have a table to check calibration - unless you are certain of the type of sensor use the table, as there are many different types, some quite (but not interchangeably) similar.
Sensors are critical for correct operation, if there's any doubt about it, replace it. (Check the calibration of the new one too...)
the red insulation appears damaged in the picture. is it?Triangle Tube Prestige Solo 110 with Trimax Controls (3x oversized)
950 sqft of WarmBoard on 3 floors, 5 loops acting as one zone0 -
That is a sensor tip I cut open to show folks what is inside.margsuarez said:the red insulation appears damaged in the picture. is it?
I found the issue.
It was the splice outside from the sensor wire to the 18 ga wire that went down stairs. I re-did the splice and sealed it up better.
ty,kcopp0