CFM through wall cavities.
Harvey Ramer
Member Posts: 2,261
How many CFM is a reasonable number to figure in a 2x4 wall cavity with studs 16" on center? Like wise 2x6?
Thanks
Thanks
0
Comments
-
-
A wall stud space return on a forced air system.0
-
-
150 cfm would give you 8 feet per second in that space. Which might be OK for smooth duct -- but the inside of a stud space isn't smooth, and your head loss would be quite high, seems to me. But that's just a gut feeling.Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England2 -
I'd be nervous figuring more than a 100 CFM but I really can't find any manual D data on the equivalent length and friction rates.0
-
Well I guess that depends on your design return static. If using .05 I'd KindaSorta say 100CFM is a good #, all that rough surface and all. . At .08 its a little more. Can you line the wall cavity with custom made trunk to get the CFM up a bit. I saw something somewhere about using the wall cavity, now where the *ell is it?1
-
My total ESP is .5 The friction rate of the duct system is .094 per/100' of effective length.0
-
how much derating should you really need to do for 2x4/2x6 and sheetrock, that's can't be all that rough, even if there's a wire or 2,
now if we're talking old rough sawn, lathe and plaster keys , , ,
then I can see quite a turbulent pathway.known to beat dead horses0 -
OK ,I see your point, but,what cfm would you recommend?0
-
-
Thanks0
-
-
Manual D 3rd Edition, Appendix 3, Fitting Equivalent Lengths, Group 7 Panned Joists and Panned stud return air fittings. page 163, Reference Velocity = 700 FPM, Friction rate = 0.08 IWC per 100ft. 200 CFM maximum in stud space, 400 CFM maximum in Joist space.
It Doesn't say anything about a 2x6, I would Guess around 300 CFM, unless they are only talking about 2x6 stud space, But I don't think so.....
I have not opened that book in a while but is sitting right behind me where it belongs. I used to have it on a PDF can't find it now.
Contact me if you need some more help....1 -
Found it, if you can open excel spreadsheets go to http://www.acca.org/standards/acca-speed-sheets/
Download the speed sheet for Manual D and open the G7 tab.3 -
Thanks! Very helpful!NJ, Designer said:Found it, if you can open excel spreadsheets go to http://www.acca.org/standards/acca-speed-sheets/
Download the speed sheet for Manual D and open the G7 tab.0 -
OK ALL WELL AND GOOD, NOW!What does that give you for an UN-panned chase,Mr.Harvey? I'm lowerrrr down in the trenches than you!0
-
Welll.... I really don't know how you would figure that one out. Unless the pressure drop was large enough to take a physical measurement.0
-
Since there is no roughness index for unpanned air spaces, it is safe to assume unpanned spaces have the same friction rate as does duct liner.0
-
You normally wouldn't want to use a 2 x 6 studs space for return air because no one would ever use an exterior wall for return air. Unless of course you don't mind having No insulation in that stud space or really hot or really cold return air temp on extreme dayson 2 x 4x16 studs space I usually account for 150-175 CFM at .05 static or 225-250 at .1 static. the legnth doesn't matter it can be 10' or 100'0
-
-
-
Welcome to HeatingHelp.com Doogie Howser , oh sorry , RyanYou didn't get what you didn't pay for and it will never be what you thought it would .
Langans Plumbing & Heating LLC
732-751-1560
Serving most of New Jersey, Eastern Pa .
Consultation, Design & Installation anywhere
Rich McGrath 732-581-38330 -
40 cfm if your lucky......0
-
I like the ductulator for quick refrences. if you want to engineer this to an exact science, there are books for that.
my quick math is, 0.5" static on the return, 4" stud (actual 3-1/2" stud) by 16" centers (subtract 1-1/2") would be 3-1/2x14-1/2 = to 50-3/4" free air space. plug that into ductulator, aprox 480cfm @ about 1500fpm. oh boy that does not sound realistic, but if your fan can pull that wall down that low, it might be a bit loud at the register!
for 2x6 wall cavity, about 950cfm @ 520 fpm.
anyone disagree with these numbers, for a loose observation?0
Categories
- All Categories
- 86.3K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 53 Biomass
- 422 Carbon Monoxide Awareness
- 90 Chimneys & Flues
- 2K Domestic Hot Water
- 5.4K Gas Heating
- 100 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 64 Pipe Deterioration
- 917 Plumbing
- 6.1K Radiant Heating
- 381 Solar
- 14.9K Strictly Steam
- 3.3K Thermostats and Controls
- 54 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements