Can loose fitting insulation cause water hammer
Fizz
Member Posts: 547
Recently had lateral pipe replaced, and new insulation is 1/2 too big(1" pipe, 11/2" insulation). Now there is water hammer. Can this be due to loose fit of insulation?
0
Comments
-
I'd say no. check that any existing piping didn't change pitch when new pipe was replaced. Double check pitch on new pipe.Fizz said:Recently had lateral pipe replaced, and new insulation is 1/2 too big(1" pipe, 11/2" insulation). Now there is water hammer. Can this be due to loose fit of insulation?
0 -
No, it's not going to cause water hammer but it won't do much good as insulation unless you cal fill up the excess space. I'll bet something got moved during the repair that changed the slope of a pipe somewhere.
Is the new pipe smaller than the old pipe? If it is there is a chance it's to small to handle the steam and condensate.
BobSmith G8-3 with EZ Gas @ 90,000 BTU, Single pipe steam
Vaporstat with a 12oz cut-out and 4oz cut-in
3PSI gauge0 -
Was the pipe replaced with the same iron pipe or did they use copper?0
-
Copper could elongate with the heat, and cause a change of slope, making a dip in the pipe where water could collect, and interfere with the steam.--NBC0
-
Actually the pipe was a re-pipe of upstairs radiator from a different lateral. The pipe is iron. Pitch seems ok. Original lateral had too much edr attached so we repiped radiator to different line and it worked.0
-
If this is a different lateral (I assume it is a horizontal pipe) then was anything done to the one that now has hammer, other than adding insulation? The insulation, in and of itself won't cause hammer. What else has changed on this specific lateral? Something has changed there, caussing water to pool in that area.Fizz said:Actually the pipe was a re-pipe of upstairs radiator from a different lateral. The pipe is iron. Pitch seems ok. Original lateral had too much edr attached so we repiped radiator to different line and it worked.
0 -
The pipe with the hammer is the one replaced. Now the hammer(I assume it's hammer), has more of a clicking sound, not loud. We tapped this pipe off a different run-out from main. There is one other radiator on a different lateral off same run-out. Both work well.0
-
Are you sure the noise is not expansion/contraction? It the pipe against a floor joist or stud ar touching anything else?0
-
If it's more of a clicking sound, odds are it's expansion...Br. Jamie, osb
Building superintendent/caretaker, 7200 sq. ft. historic house museum with dependencies in New England0 -
+1Jamie Hall said:If it's more of a clicking sound, odds are it's expansion...
0 -
That makes more sense! Thanks for input.0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 89 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements