Leaking and rusting radiators
Clancy11
Member Posts: 2
Has anyone had problems with Myson Decor leaking and rusting radiators? The manufacturer is trying to tell us its our installer's fault, although the manufacturer has changed the design since ours was installed I believe to mitigate the leaking problem. Our installer is very meticulous and experienced and followed installation instructions exactly, flushed the system properly.
0
Comments
-
How were the connections sealed? I have seen similar results when installers who thought they knew better used pipe dope and/or Teflon tape on the BSP threads.0
-
Our installer says he used both. Should he have done something different? Thank you0
-
That may well be. But one of those plugs is factory applied and it leaks too.SWEI said:How were the connections sealed? I have seen similar results when installers who thought they knew better used pipe dope and/or Teflon tape on the BSP threads.
I've never seen any specific instructions from European manufacturers on special considerations for their equipment installed on this side of the pond. And many European manufacturers have a proclivity to sell to anyone who is West of the 50th Meridian, shutting out the very ones (us) who know how to properly install equipment. If it takes special adapters to connect that equipment in the country it is sold in, the manufacturer has an obligation to provide it.
I've repaired or replaced things like that "done by others" where adequate and properly applied Teflon Tape and the correct pipe sealant compound, or RTV silicone sealant solved any leak that appeared. That method isn't in any I/O manual I have ever seen.
Just what exactly is the proper (secret) procedure for connecting that European fixture to American sizes?
0 -
Another point to ponder.
If the system is on well water, and it is "Normal" well water, it will eat right through that nice fancy European Powder Coated Enameled steel baseboard.
Right pronto, it will. A leak that looks like that, think what it looks like on the inside. Be interesting to see a water report on that well for sodium and chloride levels. PH and Iron too.1 -
As Chris pointed out, test your water.
All of the panel radiators we have installed include a plug and a coin vent in a small package. The radiators have four ports. The installer connects supply, return, vent, and plug as needed.
Straight pipe threads are intended to be used with an anaerobic threadlocker. Myson currently supplies Loctite 565 with their radiators. We had a 50+% leak rate on a job where one team of plumbers decided to employ their standard Rectorseal #5 plus PTFE tape recipe instead of reading the instructions.0 -
-
What did they use for tubing? Copper? Barrier pex? Or in the case of one job that I am presently looking to do non barrier polybutylene.... Did they add any water treatment? How old?0
-
As expensive as those Powder Coated steel baseboards are, and the tendency for many to know more than the manufacturers, and never read instructions, the manufacturers should include two flush bushings to adapt from the straight pipe thread to American tapered thread.SWEI said:As Chris pointed out, test your water.
All of the panel radiators we have installed include a plug and a coin vent in a small package. The radiators have four ports. The installer connects supply, return, vent, and plug as needed.
Straight pipe threads are intended to be used with an anaerobic threadlocker. Myson currently supplies Loctite 565 with their radiators. We had a 50+% leak rate on a job where one team of plumbers decided to employ their standard Rectorseal #5 plus PTFE tape recipe instead of reading the instructions.
When I go to vote, they always provide a pencil to mark the ballot. A couple of adapters on the bag isn't going to kill the sale.
0
Categories
- All Categories
- 86.2K THE MAIN WALL
- 3.1K A-C, Heat Pumps & Refrigeration
- 52 Biomass
- 422 Carbon Monoxide Awareness
- 88 Chimneys & Flues
- 2K Domestic Hot Water
- 5.3K Gas Heating
- 99 Geothermal
- 156 Indoor-Air Quality
- 3.4K Oil Heating
- 63 Pipe Deterioration
- 910 Plumbing
- 6K Radiant Heating
- 380 Solar
- 14.8K Strictly Steam
- 3.3K Thermostats and Controls
- 53 Water Quality
- 41 Industry Classes
- 47 Job Opportunities
- 17 Recall Announcements